    Isetech

    PV Suppliers?

    you could add loose connections to that list.

    Isetech Yesterday, 08:18 PM Go to last post
    Isetech

    Neutral/earth bridging method.

    Only if the bond is permanent, nothing wrong with installing an ELU if a relay is used. the neutral is only earthed when in islanding mode.

    Isetech Yesterday, 08:16 PM Go to last post
    Derlyn

    Neutral/earth bridging method.

    7.16.4.5 makes it illegal to supply an inverter through an ELU on it's input side.


    7.16.4.5 The neutral shall not be earthed beyond

    Derlyn Yesterday, 12:26 PM Go to last post
    Isetech

    Neutral/earth bridging method.

    The comment about the ELU has nothing to do with the contactor/relay, if you do a permanent bond and fit an ELU on the input side of the inverter it will

    Isetech Yesterday, 11:21 AM Go to last post
    GCE

    PV Suppliers?

    Most burnt connections etc I have seen are bad workmanship , strands cut off before fitting into lugs , AC equipment used in place of DC , DC CB used

    GCE Yesterday, 10:31 AM Go to last post