Thread: How to isolate an earth leakage problem

  1. #31
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I did make an information thread about earth leakage tripping faults, it was aimed more at DIY'ers but it might be worth a read for ideas.

    What actual tests have you done on the circuits and what were the results ie insulation (megger) tests of the final circuits and Ze (or Zdb) etc. Did you try an actual proper ramp test of the earth leakage? What loads is the earth leakage supplying?
    _______________________________________________

    _______________________________________________

  2. #32
    Full Member MullerR's Avatar
    Join Date
    Jan 2016
    Location
    Lady Grey
    Posts
    44
    Thanks
    3
    Thanked 6 Times in 5 Posts
    Hi Andy.

    I Read your article about the Earth leakage tripping faults and I think I still have a lot to learn. The Information is of much help to me. Unfortunately I have not done any tests like the Insulation resistance and ramp test as I did not have my testers with me, We were visiting the people and the only tester I had was my multimeter and ELCB/polarity tester. Thanx for the info on the testers as well, when I did my trade, testers like the Ramp tester and earth leakage clamp tester were not mentioned to us as important to have testers, but thanx to you I will have to buy me.

    The house is quite old and there is not much electronics in the house, or shall I Say not more than there were in the past, just the normal, freezers(2), deep freeze, Microwave, TV, Decoder, PC... The installation also is old and the earth leakage feeds all the circuits (Plugs, Lights, Stove and geyser). I believe I will be visiting again during this month, but the main thing that buggers me is the fact that it dont even want to trip when tested with a ELCB tester, but the RCD in the Kitchen that is in the ready board trips when tested as well as the one in the garage.

  3. #33
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,663
    Thanks
    3,309
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by MullerR View Post
    but the main thing that buggers me is the fact that it dont even want to trip when tested with a ELCB tester
    Assuming you've used a plug socket tester which didn't show any faults on the socket outlet, I've heard of loose terminal connections causing this sort of problem.

  4. #34
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Being an old installation there is possibly bad earth continuity in the house, quite probably a floating earth which will still light the lamp of the polarity tester. Also confirm that the socket outlet you are testing actually has ELCB protection. It could be a new circuit added in with the neutral connected to the top of the ELCB.

  5. #35
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    L-N reversal through the earth leakage could cause it possibly not to trip if there was no load current through it during testing plus it could make it not trip on the test button. Also I've come across weird intermittent ''not tripping'' issues with RCD's which have the supply and the load side of them wired the wrong way around.

    My favorite one is that in theory a small low insulation fault N-E on one of the circuits being supplied could also cause the test button not to work but the earth leakage unit itself could still be fine. I've yet to come across this in real life but it could certainly cause some headscratching if it ever did occur .

    It's all guesswork until you do the usual tests when you next visit.
    _______________________________________________

    _______________________________________________

  6. #36
    Full Member MullerR's Avatar
    Join Date
    Jan 2016
    Location
    Lady Grey
    Posts
    44
    Thanks
    3
    Thanked 6 Times in 5 Posts
    Thanx guys. With my next visit i will be doing some tests and make sure to get behind this problem.

  7. #37
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    When would a fault before, (upstream) of the E/L device cause the E/L to trip? Meaning there is no fault under the E/L (L & N disconnected at E/L terminals load side). Ramp test clear on E/L 27Ma @40Ms. TN-C-S supply.

  8. #38
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by ACEsterhuizen View Post
    When would a fault before, (upstream) of the E/L device cause the E/L to trip? Meaning there is no fault under the E/L (L & N disconnected at E/L terminals load side). Ramp test clear on E/L 27Ma @40Ms. TN-C-S supply.
    I see you treated yourself to a ramp tester, I'm jealous, I haven't bought any new testers for several months now .

    How often is it tripping? Is it regular as clockwork or is it random?

    It's not one of the old types of RCD as per pic below that has an earth reference wire on it by any chance? If it is there could be a slim chance that an earthing fault on the supply side could present parallel paths that could cause a fault in a neighboring property to cause the RCD to trip.

    Click image for larger version. 

Name:	untitled1.jpg 
Views:	335 
Size:	48.3 KB 
ID:	6127

    I've only ever once experienced an external problem causing RCD nuisance tripping and it was an RCD that tripped almost every evening when the streetlight outside the house switched on. I can't for the life of me remember what make it was but I replaced the RCD with an identical new one and it also did the same. After another replacement of a different make it stopped happening. I did some power quality monitoring at the supply and couldn't see any evidence of transients that would point to arcing when the streetlight switched on so eventually decided it was a harmonics issue with that particular brand of RCD but I could never prove it.

    I've heard hearsay of poor connections/arcing on the council supply side causing RCD's to trip as well so maybe check the Ze and the neutral-earth voltage of the supply.
    _______________________________________________

    _______________________________________________

  9. Thanks given for this post:

    ACEsterhuizen (14-Jan-16)

  10. #39
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    Thanks Andy. New SABS approved Schenker SP E/L with L N only no earth. (tried 2 new ones). Total random intermittent tripping. Ze (external impedance all ok when tested (0.17Ω).

    You were spot on. Poor connection & arcing N/E on council supply in street feeding to house. Municipality came out open their street box and the N/E was arcing, burning, loose connection, hanging on a thread. Fixed it, all OK, 8 hrs no tripping.

    But why? i don't understand why a fault before the E/L would cause it to trip.


    Yes i am
    Last edited by ACEsterhuizen; 15-Jan-16 at 06:43 AM. Reason: capitilized letters

  11. #40
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    TBH I'm not sure why it would cause an RCD to trip, there's no current imbalance on the load side which is the criteria for tripping. I'd guess it's an anomaly with the internal electronics maybe.

    How's the tripping fault, is it still holding?
    _______________________________________________

    _______________________________________________

Page 4 of 5 FirstFirst ... 2345 LastLast

Similar Threads

  1. Geyser not on earth leakage
    By Goobie in forum Electrical Contracting Industry Forum
    Replies: 21
    Last Post: 03-Jan-19, 05:44 PM
  2. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  3. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM
  4. Random earth leakage problem
    By BillH in forum Electrical Contracting Industry Forum
    Replies: 39
    Last Post: 23-Jan-12, 09:37 PM
  5. CBI earth leakage units
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 29-Oct-09, 12:44 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •