    Guys, what would cause a City Power breaker to trip randomly?
    It goes for several hours and trips around twice a day at different times.
    Single phase 80A breaker.
    Amps pulled way way under spec - 34A.
    House DB not tripping.
    Customer is postpaid.

    Have disconnected the feed cable from CP and the DB and Meggered it - all good. No cable fault. CP was in attendance but didn't have an insulation tester.

    Any ideas?

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,571
    Thanks
    110
    Thanked 149 Times in 141 Posts
    Faulty breaker.

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,571
    Thanks
    110
    Thanked 149 Times in 141 Posts
    Those random times you were referring to is probably when the geyser or some other heavy load kicks in and the faulty breaker then trips.

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,571
    Thanks
    110
    Thanked 149 Times in 141 Posts
    Take the back end of your screwdriver and tap that breaker lightly on it's side. If it then trips, it's shot.

    This is a trick that my tutor taught me in the 70's and it has been usefull on many occasions throughout the years.

  5. Thanks given for this post:

    Andrew_van_Zyl (11-Apr-24)

  6. #5
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    123
    Thanks
    54
    Thanked 9 Times in 8 Posts
    Quote Originally Posted by Derlyn View Post
    Take the back end of your screwdriver and tap that breaker lightly on it's side. If it then trips, it's shot.

    This is a trick that my tutor taught me in the 70's and it has been usefull on many occasions throughout the years.
    Thanks Brother. Good suggestion. The breaker stood up to some quite enthusiastic tapping but stayed on. CP replaced the cb recently. Out of ideas here

    Sent from my SM-A226B using Tapatalk

  7. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,296
    Thanks
    36
    Thanked 314 Times in 263 Posts
    Been thinking on this one - Do you have an isolator or CB as mains in the DB

    If city power is 80Amp - I would put a 60 amp in the DB on mains to see if that trips first

    My gut tells me you have a cable fault that is tripping when it blows clear which is why your megga test does not pick up an issue - An hour or so later once water has got back into the problem area it will sit and short until it blosws again
    Test after and hour or 2 of being on.

    Had similar on 2 x 120sqmm in parallel - Cable must have been damaged years ago and took almost 15 years before the fault become a complete nuisance - It was under a concrete yard and we were just lucky that while we were standing there we saw wisp of smoke come out between concrete joints - dug down and found the cable fault.

  8. Thanks given for this post:

    Andrew_van_Zyl (20-Apr-24)

  9. #7
    Bronze Member
    Join Date
    Mar 2022
    Location
    Little Falls, Roodepoort
    Posts
    123
    Thanks
    54
    Thanked 9 Times in 8 Posts
    Good suggestion GCE - Thank you. Weirdly the problem has gone away and the client is less noisy. I will re-visit this if and when.

    Lol at wisps of smoke - generally a sign of trouble!

Similar Threads

  1. Circuit breaker tripping but not EL
    By Andrew_van_Zyl in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 21-Oct-23, 06:59 PM
  2. Earth Leakage Breaker (RCD) Tripping
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 33
    Last Post: 14-Jul-23, 02:53 PM
  3. [Question] Overheating Wire from City Meter back to Eskom power supply
    By Angelojp22 in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 24-Nov-22, 04:05 PM
  4. Pump supply connected to City Power point of supply board
    By kosmonooit in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 10-Dec-21, 10:10 AM
  5. Jhb City Power Contractors
    By kosmonooit in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 11-Aug-18, 09:37 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •