Results 1 to 3 of 3

Thread: ECC Armoured Cable Terminations

  1. #1
    Full Member
    Join Date
    Feb 2012
    Location
    Cape Town
    Posts
    41
    Thanks
    0
    Thanked 3 Times in 3 Posts

    ECC Armoured Cable Terminations

    Hey guys

    I have been to numerous cable manufacturers to discuss the correct termination of an ECC cable. It amazes me that not one manufacturer knows how. When looking at the the regulations regarding this there is quite a bit.
    Would you agree that the an ECC cable should be glanded off and terminated in the same way as a normal SWA cable would be? We have been told that the copper armoring should run through the gland and connect to the consumers earth bar. Surely if we gland of the cable and the gland connects to the steel enclosure and we use an earth tag this will be sufficient earthing?
    This eliminates the need for a separate earth to be installed. Especially in a high crime area.
    We have done the PSCC calculations and loop impedance and we are well under the maximum permissible values.
    Could one of you gents or ladies enlighten us as to how this cable should be terminated if the above method is incorrect?

    Below are parts of the SANS 10142-1 sections that we followed:


    6.3.7.3 Any armouring or sheathing shall be terminated in or on
    equipment. Armour wires shall be terminated by a clamp or gland in such
    a way that
    a) pressure is not applied to insulating material, and
    b) there is an earth tag washer (or similar) for connecting to the earth
    continuity conductor.

    6.12.1
    NOTE Where the armouring of a cable is used as the earth continuity path, the
    resistance of the earth continuity path shall not exceed the appropriate value given in
    table 8.1; it may be necessary to replace some of the steel wires with tinned copper
    ones or to use a supplementary earth continuity conductor.

    M.2.2 – TN-S system earthing
    The protective conductor (PE), which is connected to the source earth, is
    either a separate conductor or the armour of the cable if the resistance of the
    armouring is such that the earth fault loop impedance complies with the
    requirements of 8.7.5.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,925
    Thanks
    576
    Thanked 935 Times in 756 Posts
    I've only come across the ECC SWA cabling on a few occasions and we've always terminated it as you would a standard SWA cable. I've never seen the copper armour strands taken through the gland as you describe.
    _______________________________________________

    _______________________________________________

  3. #3
    Email problem
    Join Date
    Oct 2012
    Location
    DURBAN
    Posts
    23
    Thanks
    0
    Thanked 3 Times in 2 Posts
    It common practice in industry if one uses 3 core ECC cable eg motor circuit

Similar Threads

  1. [Question] Cable depth
    By ElectricalContractorGuy in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 26-Oct-15, 11:33 AM
  2. Cable sizes?
    By Greg in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 09-Aug-11, 11:42 PM
  3. Lead cable
    By ColinK in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 26-Jul-11, 07:50 PM
  4. cable sizes
    By bergie in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 20-Mar-11, 08:50 PM
  5. [Article] Exe cable glands for braided cable
    By Master Electrician in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 26-Aug-10, 02:47 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •