'In' is the current rating of the MCB which in your case is 400A I assume.
'Io' is the course setting for the 'long time' protection threshold
'Ir' is the fine setting for the long time protecton.
You work out you overload protection using In x Io x Ir.
Isd is the threshold of the short time pickup. Some breakers you can adjust the time delay on the Isd point (0-0.5 secs max usually) but I don't see any adjustment on yours. .
Also some breakers have adjustment on the Ii threshold which is the point of Instantaneous short circuit protection, again yours doesn't appear to have this.