    Quote Originally Posted by hartdev@hotmail.com View Post
    1. I would say it is always best that the sub Db have its own earth leakage breaker for discrimination , to fault find etc but don't believe it is a law, just good practice, especially since some places have their entire installations on earth leakage protection.
    2. The Main CB is very seldom rated at the sum of all other circuit breakers as we take the estimated load factors into account , ie: Your geyser won't always be on when your stove is on etc you would struggle to find a residential 60amp installation with only a sum of 60amps circuit breakers installed.
    3. It should if done properly.....
    but I just took a look at your logo (diamond member) and I'm wasting my time telling you things you already know x)

    Thanks. I am a Diamond member because I have been a part of this group for many years. I am not an electrical contractor and I really appreciate your insight. And yes, I fully agree that everything should be done properly.

  2. #12
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by adrianh View Post
    A couple of stupid questions:

    1. Should a sub DB have an earth leakage breaker?
    Depends on the circuits in the SubDB. If there's socket circuits or any other types of circuit that require earth leakage protection then yes, there should be an earth leakage breaker installed (or RCBO's used instead of MCB's).
    Quote Originally Posted by adrianh View Post
    2. Will that breaker be rated at the sum of the other breakers (provided of course that all wiring is appropriately rated)
    No, highly unlikely. We work on a system of 'diversity' where it's assumed (gambled) that every circuit would never simultaneously be under full load conditions. There are rules for working out diversity in the regs.
    Quote Originally Posted by adrianh View Post
    3. Will the tripping of the sub DB EL breaker save the main DB EL breaker from tripping?
    It's poor electrical design to have an earth leakage breaker that's fed from another earth leakage breaker unless one is differently rated to the other ie one is a faster type or they both have different mA ratings otherwise it's always a lottery which one trips first and often both will trip during a fault. It's also bad design to have the supply for a SubDB run from an earth leakage breaker in the main DB.
    _______________________________________________

    _______________________________________________

  3. Thanks given for this post:

    Dave A (20-Sep-17)

  4. #13
    Diamond Member
    Join Date
    Mar 2010
    Location
    Cape Town
    Posts
    6,328
    Thanks
    426
    Thanked 977 Times in 794 Posts
    It's poor electrical design to have an earth leakage breaker that's fed from another earth leakage breaker unless one is differently rated to the other ie one is a faster type or they both have different mA ratings otherwise it's always a lottery which one trips first and often both will trip during a fault. It's also bad design to have the supply for a SubDB run from an earth leakage breaker in the main DB.

    - Does this mean that A sub DB board is wired in parallel to the main board rather than being fed off the main db board breaker - so that each board has its own separate supply, main breaker and earth leakage?

  5. #14
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The supply for the Sub DB would be via the main breaker in the main DB and a second breaker in the main DB for the subDB cable.

    Click image for larger version. 

Name:	1.jpg 
Views:	793 
Size:	60.9 KB 
ID:	6875
    _______________________________________________

    _______________________________________________

  6. #15
    Diamond Member
    Join Date
    Mar 2010
    Location
    Cape Town
    Posts
    6,328
    Thanks
    426
    Thanked 977 Times in 794 Posts
    Why are the two breakers in series with the same break current?

    Which one will break if a fault occurs in the garage at 60A?

  7. #16
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    This was just a drawing I had kicking around so I edited it for illustration.

    The garage circuit breaker would be sized according to the size of cable feeding the garage and several other factors including the installation method used for the cable and the length of the cable etc.

    It could be okay to use the same size breaker for the garage as the main breaker if the cable size was sufficient but it would be good practice to introduce 'discrimination' by making the garage breaker a faster curve than the main breaker ie the garage breaker might be a 'B curve' and the main breaker could be a 'C curve'.
    0600DB0105.pdf (first page for brief explanation)
    _______________________________________________

    _______________________________________________

  8. #17
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    What non-electrical people need to understand is that a circuit breaker is selected to match the thickness of the wire used along with other factors. It's purpose is to protect that cable. Usually in the main DB the breaker is stronger for the supply to a sub-DB because the cable is thicker. The sum of the breakers is never a consideration. Many sub-DBs' have a supply rated at below 60A in the main board, but the main switch in the sub-DB is rated at 60A. This is because a 60A Double pole isolator is cheaper. The pupose of the main switch is to isolate the sub-installation. Each circuit fed from the sub-DB should be protected by a lower rated CB than the Sub-DB supply CB in the main board. This will localise tripping to the sub-DB.

    The only device in the DB that protects the user is the ELCB. It is good practice to once a month switch off all electronic devices and press the test button on the ELCB. This will be an indication that it it still functioning. It is also wise to have it tested every two years to determine whether it still functions within the rating.

  9. #18
    New Member
    Join Date
    Mar 2023
    Location
    Joahnnesburg
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by AndyD View Post
    The supply for the Sub DB would be via the main breaker in the main DB and a second breaker in the main DB for the subDB cable.

    Click image for larger version. 

Name:	1.jpg 
Views:	793 
Size:	60.9 KB 
ID:	6875
    If the Sub-Db is fed from the main breaker Pre-Earth Leakage in the main DB, does this mean that the cable from the main DB to the garage sub-DB is not protected by an earth leakage device and that only the wiring and devices after the Sub-DB's earth leakage device are protected by the EL? Is the cable from the main DB to the Sub-DB only protected from over-current by the MCB and not protected against earth leakage?
    Could one, for example, have the EL for the sub-DB situated in the main DB enclosure as shown in this diagram?

    Click image for larger version. 

Name:	MAIN AND SUB db.jpg 
Views:	199 
Size:	18.2 KB 
ID:	8719

  10. #19
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,531
    Thanks
    106
    Thanked 146 Times in 139 Posts
    One could have the sub db fed from the earth leakage in the main db as in the diagram, however, I never do it that way. I always ensure that the sub db has it's own earth leakage. That way, if there's an earth fault on the sub db, it doesn't affect the main db.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Amp rating of incoming supply breaker
    By Gnome in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 05-Jun-17, 07:45 PM
  2. [Question] Plug circuit's neutral wire is 1.5mm, cb amp rating?
    By hartdev@hotmail.com in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 23-Mar-16, 08:14 PM
  3. Electric Heating Load Rating
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 02-Apr-09, 09:22 AM
  4. TFSA google rating
    By garthu in forum Technology Forum
    Replies: 8