    I have a question for the theory boffins.

    A recent discussion resulted from the question as to why would a 3 phase generator (portable stand alone) that is connected to a container office as the only source of supply require an earth spike in the ground. The feed from the generator is via a cable (+-6m) to the container office single phase DB.

    Any theories on this? Unfortunately I dont have any further details on the generator regarding winding configuration etc but there is a built in main switch, earth leakages (4p + 2P) and single phase circuit breakers.

  2. #2
    Bronze Member
    Join Date
    Mar 2012
    Location
    Account_Deleted
    Posts
    165
    Thanks
    122
    Thanked 23 Times in 18 Posts
    Aahhh Its easy.... just follow the regs... it "explains itself??"

  3. #3
    Full Member
    Join Date
    Oct 2012
    Location
    Durban
    Posts
    66
    Thanks
    0
    Thanked 5 Times in 4 Posts
    The regs only deal with a generator as alternate supply with the exception of a single phase generator with V-O-V configuration. I am more interested in the theory as a stand alone supply on a three phase generator with regards to an earth spike

  4. #4
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,664
    Thanks
    3,309
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    The objective is to ensure "correct operation of the protection devices, irrespective of the source of supply" (a requirement of 7.12.3.1, which deals with Neutral bar earthing).
    Essentially to achieve this you need to prevent the neutral from floating off earth, and the earth to maintain a voltage as close to ground as possible (among other things). Hence in your example you would require the earth and neutral to be bridged as close to the power source as practical, and the earth to be grounded via an earth spike.

    In the test section we have:

    8.7.6 Elevated voltage on supply neutral
    With the main switch off, measure the voltage between the supply neutral and any earth external to the installation.

    Essentially this requires corrective action if above 25 Volts and disconnection if above 50 Volts.

  5. Thanks given for this post:

    ACEsterhuizen (02-Dec-16)

Similar Threads

  1. [Question] N3 Electrical Trade Theory
    By RegElec in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 02-Feb-16, 09:20 PM
  2. Not a theory, BVRB was a Master.
    By Trickzta in forum General Chat Forum
    Replies: 2
    Last Post: 28-Jan-14, 05:46 PM
  3. To all Politicians...Simple Tax Theory
    By Alan in forum South African Politics Forum
    Replies: 2
    Last Post: 26-Jun-10, 10:24 AM
  4. An alternative theory of unions
    By duncan drennan in forum Entrepreneurship and Business Management Forum
    Replies: 1
    Last Post: 09-May-07, 10:31 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •