Page 1 of 3 123 LastLast
Results 1 to 10 of 22

Thread: Solar challenges

  1. #1
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,138
    Thanks
    57
    Thanked 101 Times in 96 Posts

    Solar challenges

    Doing normal electrical work on sites which have solar installations.

    Our standard requirement is copy of all COC's for the site, before we step foot on the site and that people is where the fights normally start.

    How do you deal with the non compliant COC's on properties where customers want you to take over the electrical and maintenance on the property ?

    Without even looking at the COC, you can already identify a list of visible non compliant issues.

    Lets say you have a 5 kw inverter and a 35 or 40 amp supply breaker, the way I see it due to the pass through current using a 2.5 mm 4 core surfix for the input and output would automatically be a code violation.

    The same with the 8 kw inverter with a passthrough current of 50 amps, with an anything form a 50-63 amp mcb supplying the inverter input, a 6 mm 4 core surfix just wouldn't cut it. We can go into details about the thin single earth wire another time.

    The solar COC is added to the original COC, which is great, but, how do you add a COC to the original if you modify all the DB's to essential and non essential?

    If the solar installer modifies every DB on the property, surely the solar COC/test report becomes the original and the original is no longer valid?

    If you look at the top of the test report, it clearly states "" Test report for DB/ supply" so if you modify the DB in any way the original test report for that DB is no longer valid?

    You would have to carry out a full test report once the DB is upgraded.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  2. #2
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,138
    Thanks
    57
    Thanked 101 Times in 96 Posts
    By the way, as we all know, the minute you touch any part of that elctrical, you become liable for everything that is or was wrong with the installation.

    It is different if you add a solar system and new Sub DB's which the essential/inverter output is not located in or connected in the main DB.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  3. #3
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    902
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Exactly. Nobody looks at what the pass-through current is, let alone make provision for it.

  4. #4
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,138
    Thanks
    57
    Thanked 101 Times in 96 Posts
    Electricians cant even tell the difference between a PZ and PH screwdriver or a standard mcb vs a D curve and you expect them to understand passthrough current?

    It could explain why green card holders (with a whole 3-5 days worth of training) are the preferred solar installers.



    Quote Originally Posted by Sparks View Post
    Exactly. Nobody looks at what the pass-through current is, let alone make provision for it.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,287
    Thanks
    36
    Thanked 310 Times in 261 Posts
    Quote Originally Posted by Sparks View Post
    Exactly. Nobody looks at what the pass-through current is, let alone make provision for it.
    I don't quite understand what provision you talk about with regards to pass through current

  6. #6
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    902
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Quote Originally Posted by GCE View Post
    I don't quite understand what provision you talk about with regards to pass through current
    Using correctly rated breakers and cables instead of underrated breakers and cables would be taking precaution and making provision. I am currently redoing new installations, done by a green card holder brought from COCT to the Eastern Cape by the developer of a new residential complex. The electrical contractor has very limited knowledge of SANS, to the extent that an ECA official has abused his position and made ridiculous demands for changes to the installation which are not dictated by SANS. I have been contracted by the contractor to "rectify" the "faults", but have informed him which items are not in contravention. As long as he keeps paying me, I will do as he asks, albeit unnecessary.

  7. #7
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,287
    Thanks
    36
    Thanked 310 Times in 261 Posts
    Quote Originally Posted by Sparks View Post
    Using correctly rated breakers and cables instead of underrated breakers and cables would be taking precaution and making provision. .
    Pass through current is in my opinion not a rating that should be taken into account for normal operation of the inverter .
    CB should be rated at the load that is intended to used under normal conditions and the wire size would follow.

    What we are seeing is guys installing 5kw inverters along with a 5KWH battery and then all protection is based on the pass through current of a 10kw system.As soon as there is a dip in power/loss of power/loadshedding the inverter and battery are trying to pick up the pass through current and you end up with a low DC voltage fault which indicates that the actual inverter was overloaded

    We are also seeing all socket outlets and light circuits in a domestic dwelling running off the inverter and the kitchen has a dishwasher , wash machine, kettle , dishwasher etc and the worst is when they include the geyser and stove.

    Owners are then told to make sure that they don't use to many appliances at the same time which in my opinion contravenes Clause 7.12.2.4

    The battery warranty is gone because the warranty terms state that on average the battery should only discharge at 0.5c even though spec says 1c and more than 3 overloads voids warranty

    An inverter is a generator not an appliance - We would never load a generator at 100% load and expect it to last .

    Then we also have clause 5.5.2 and 5.3.1 with reference to Annex c which stipulates sizing of power requirements for socket outlets



    SANS 10142-1 ed3.1
    7.12.2.4 Where the alternative supply is intended to provide a supply to an
    installation that is not connected to the main supply, or to provide a supply as
    a switched alternative to the main supply, the capacity and operating
    characteristics of the alternative supply shall be such that danger or damage
    to equipment does not arise after the connection or disconnection
    of any
    intended load as a result of the deviation of the voltage or frequency from the
    standard range. Means shall be provided to automatically disconnect such
    parts of the installation, as may be necessary if the capacity of the alternative
    supply is exceeded


    5.5.2 Harmful effects by electrical equipment
    Electrical equipment shall be so designed and arranged that any damage as
    a result of a fault be localized as much as possible. The equipment shall not
    have harmful effects on other equipment or on the power supply during normal
    service (including switching operations)
    . Factors that can lead to harmful
    effects include
    a) the power factor,
    b) inrush current,
    c) asymmetrical load, and
    d) harmonics


    5.3.1 Estimated load
    The load of an installation shall be estimated to determine the type and
    capacity of the required electricity supply.
    NOTE 1 Annex C gives an example of estimating the load for residential installations
    but the method is not to be regarded as an exact method.
    NOTE 2 The supplier may have special requirements for large installations and for
    installations that need special consideration.

  8. #8
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,287
    Thanks
    36
    Thanked 310 Times in 261 Posts
    Quote Originally Posted by Sparks View Post
    to the extent that an ECA official has abused his position and made ridiculous demands for changes to the installation which are not dictated by SANS. I have been contracted by the contractor to "rectify" the "faults", but have informed him which items are not in contravention. .
    Would be interested to know what the demands where made and what you deem not be in contravention

  9. #9
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    902
    Thanks
    21
    Thanked 127 Times in 96 Posts
    Quote Originally Posted by GCE View Post
    Would be interested to know what the demands where made and what you deem not be in contravention
    He gave a whole list. No bridges in the DB smaller than 16mm. 2.5mm cable may not be protected by 25A CB. The motivation was that the socket outlet is only rated at 16A, yet it was insisted on that 20A CBs' be used. Cables in the roof had to have pieces of conduit secured to all the trusses to protect cables where they went over them, despite such occurrences not being where anyone would normally walk in the roofspace thus, no undue exposure to damage. A number of similar demands were made which my poor memory does not recall offhand. I concentrated more on just doing what was asked and I was being paid for.

  10. #10
    Silver Member
    Join Date
    Mar 2008
    Posts
    354
    Thanks
    5
    Thanked 50 Times in 43 Posts
    This the thing with the CoC story. You can't MAKE someone pay for a CoC.
    Or MAKE them pay for work to make it compliant.

    Yet if I'm the last one to touch a DB it's my fault ����.

    Still not entirely sure where we stand.
    We did a 12kw Sunsynk install on a, I'd guess, R6000000 house.

    There was a CoC, which didn't look bad and we did a few basic tests before starting (Earth fault loop, visual checks etc)

    Install was done over 3 days, commissioned - no worries.
    Start doing proper testing and find a shit show (no earth readings etc). Then twist and tape special hidden.
    Spent another 3 days fixing bits and pieces to get it to point where is could be signed off but eventually enough was enough.

    Gave the customer a report on what we had done and other things that needed attention but they weren't interested (in paying for additional works needed) and we refused to issue the CoC.

    They still paid for the solar install but they don't have a CoC from us. Like I said - can only advise, can't make them have the work done.

Page 1 of 3 123 LastLast

Similar Threads

  1. Solar backup system challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 27-Mar-24, 09:48 AM
  2. Solar challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 21-Jul-23, 08:26 AM
  3. Solar install challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 11-May-23, 03:00 AM
  4. Backup/solar challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 16-Feb-23, 10:14 AM
  5. Solar/inverter/batteries installation challenges
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 01-Dec-22, 03:53 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •