Page 3 of 3 FirstFirst 123
Results 21 to 22 of 22

Thread: Neutral/earth bridging method.

  1. #21
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,554
    Thanks
    109
    Thanked 147 Times in 140 Posts
    Quote Originally Posted by Isetech View Post
    The comment about the ELU has nothing to do with the contactor/relay, if you do a permanent bond and fit an ELU on the input side of the inverter it will trip.
    7.16.4.5 makes it illegal to supply an inverter through an ELU on it's input side.


    7.16.4.5 The neutral shall not be earthed beyond any earth leakage unit.

  2. #22
    Platinum Member
    Join Date
    Mar 2022
    Location
    South Africa
    Posts
    2,142
    Thanks
    58
    Thanked 101 Times in 96 Posts
    Only if the bond is permanent, nothing wrong with installing an ELU if a relay is used. the neutral is only earthed when in islanding mode.



    Quote Originally Posted by Derlyn View Post
    7.16.4.5 makes it illegal to supply an inverter through an ELU on it's input side.


    7.16.4.5 The neutral shall not be earthed beyond any earth leakage unit.
    Comments are my opinion, unless regulations are attached to support the comment. This is social media, not a court room.

Page 3 of 3 FirstFirst 123

Similar Threads

  1. Neutral Earth - more info
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 25-Feb-23, 03:41 PM
  2. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM
  3. High neutral earth reading
    By Thys LOW Elektries in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 27-Mar-22, 02:26 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •