    Will a 415v transformer work for a 400v machine

    Good day

    Looking for any legal document/links etc to support the tolerance issue which are reasonable in the electrical trade and meet any regulatory standards.

    Thanks in advance

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,284
    Thanks
    34
    Thanked 309 Times in 261 Posts
    Quote Originally Posted by Badabing View Post
    Good day

    Looking for any legal document/links etc to support the tolerance issue which are reasonable in the electrical trade and meet any regulatory standards.

    Thanks in advance
    SANS 10142-1 states voltage



    5.4.2 Voltage
    The equipment shall be suitable for operation on the maximum steady (r.m.s.)
    voltage and overvoltage to which it is likely to be subjected. Equipment shall
    be rated in accordance with the intended application for use on one of the
    following voltages used in South Africa:
    a) A.C. circuits:
    1) standard voltages at a point of supply of Amdt 1
    i) 230 V single-phase,
    ii) 230/400 V three-phase four-wire, and
    a tolerance of ± 10 % on these voltages.
    NOTE For certain equipment it may be necessary to consider the lowest voltage
    that is likely to occur.
    2) declared voltages of 525 V three-phase three-wire is a commonly used
    voltage and the tolerance is ± 5 %.
    NOTE Declared voltage is the voltage declared by the manufacturer up to the
    maximum of 1 000 V.
    b) D.C. circuits:
    1) preferred voltages of
    i) 12 V,
    ii) 24 V,
    iii) 48 V,
    2) other voltages of
    i) 60 V,
    ii) 80 V,
    iii) 110 V,
    iv) 220 V,
    v) 250 V,
    vi) 500 V, and
    the tolerances on the above d.c. voltages are determined by the
    application.
    c) Voltages on control circuits should preferably not exceed 230 V a.c. or
    110 V d.c.

Similar Threads

  1. 3 wire transformer
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 15-Oct-20, 11:14 AM
  2. UPS Transformer
    By Andrew G in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 29-Jan-18, 09:16 AM
  3. 3 -Phase Transformer
    By DannyTee in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 19-Nov-17, 09:15 PM
  4. help on transformer size
    By Jaboel in forum Electrical Contracting Industry Forum
    Replies: 10
    Last Post: 30-Jun-16, 06:40 PM
  5. [Question] Mini transformer
    By Martinco in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 24-Jul-14, 10:47 AM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •