TBH It's not that rare, I get stumped quite regularly. I've never worked on a Dahlander Motor installation but I live in hope.
You can fully enclose a VFD in an enclosure without ventilation but there strict manufacturer recomendations on how much surface area the enclosure must have to allow the heat to be dissipated and it must be of metal construction. The enclosure size is also relative to external ambient temperatures so if it's being used outdoors in a ventilated and shaded area then it should be a sensible size. The last drives we had to fully enclose in a plant room (44 degrees C ambient) the enclosure needed to be 1000 x 1200 x 500mm and mounted on spacers to hold it off the wall in order to fulfil the heat dissipation requirements. We also installed a small tangential blower similar to an air curtain above them just to play it safe.