Page 1 of 2 12 LastLast
Results 1 to 10 of 20

Thread: Din rail breakers fake or not

  1. #1
    Bronze Member
    Join Date
    Mar 2013
    Location
    Cape Town
    Posts
    111
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Din rail breakers fake or not

    Is there any opinion regarding LS din rail circuit breakers from voltex, they have the orange toggle. I was called for wires that was melting and when I got there it was a couple and melted before it enters the conduit, this is probably due to over current, I don't know what else could cause it and the breakers never tripped. Are there fake LS din rail breakers out there and how would they be recognised as these were bought from an electrical wholeseller?

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,490
    Thanks
    138
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    At the time you were called out, or during the fault, did you measure the current?
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Bronze Member
    Join Date
    Mar 2013
    Location
    Cape Town
    Posts
    111
    Thanks
    0
    Thanked 0 Times in 0 Posts
    No, the owner got someone else to fix cause I'm out of town. I can only think that the main switch at the meter could be faulty and / the din rail breakers, I've foun CBI breakers that was a fake cause someone got shocked and it never triped out. The date on the back of the breaker was stamped with a mashine and not a hand stamp. That's the sighn of a fake CBI breaker but I don't know what the sighn is with these ones.

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    One of the easiest ways to spot a fake is familiarity with the product. I've spotted fakes in the past by the different feel of the breaker when you operate the toggle, also the different weight and the way it flexed when the terminals were tightened. I don't use LS breakers so I can't give specific advice but almost every manufacturer nowadays has info about how to spot fakes on their website and to be honest if the manufacturer doesn't have a website then I'd avoid them like the plague.

    With overheating damage to the insulation it's normally easily spottable if it was caused by a poor termination on the breaker. If the damage occurred on the wire away from the breaker where it enters the conduit then maybe the wire was stretched or otherwise damaged as it was installed.

    Unfortunately it's not easy to test the calibration of MCB's, you need a current injection set and the appropriate instrumentation to plot the disconnection time curve and this equipment isn't generally available so if they look good, feel good and smell good you've just got to assume they're going to operate. This is a leap of faith I usually reserve for recognised brand names only.
    Last edited by AndyD; 05-Oct-13 at 02:22 AM. Reason: spelling
    _______________________________________________

    _______________________________________________

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I don't think an LS circuit breaker has to be a fake, the cheap crap they are selling could just as well be fake the quality is such rubbish.

    CBI earth leakage unit being sold must be fake because they don't last longer than 2 years, I have some installation where the CBI earth leakage unit is still working after 20 years, I replace one of the old E/L after 20 years and the new one is replace db before the other old ones are replaced in the same panel.

    I don't use them (AC/DC)but I have heard from other contractors complaining at the wholesalers, that the AC/DC earth leakage unit is the worse at the moment and it seems CBI comes a close second. I stopped using CBI and now replace with chint, haven't had any problem to date.

    By the way a circuit breaker is not a human protective device and will not trip if you are shocked unless you create a dead short or the current exceeds the current rating of the breaker, which will result in a death if more than a couple of mA.

    It sounds to me like there was a loose connection which could have caused intermittent tripping which they didn't inform you about, or the circuit breaker was incorrectly selected which resulted in the wire melting form overloading.

    A question, you mentioned that a couple of wires melted before they entered the conduit, where these circuits all fed from the same circuit breaker or are you referring to an earth leakage unit? If there are multiple circuit burning then I would suggest you do an investigation into the cause, soon.

  6. #6
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts

    Thumbs down

    Quote Originally Posted by ians View Post

    I don't use them (AC/DC)but I have heard from other contractors complaining at the wholesalers, that the AC/DC earth leakage unit is the worse at the moment and it seems CBI comes a close second. I stopped using CBI and now replace with chint, haven't had any problem to date.
    I also had problems with AC/DC Earth Leakages. It takes so long to shop there, you'd imagine you would at least receive a product that works at the end of the wait
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  7. #7
    Silver Member
    Join Date
    Mar 2008
    Posts
    352
    Thanks
    5
    Thanked 50 Times in 43 Posts
    Quote Originally Posted by Leecatt View Post
    I also had problems with AC/DC Earth Leakages. It takes so long to shop there, you'd imagine you would at least receive a product that works at the end of the wait
    ACDC - gave up on them. 9 times out of ten I would wait longer for the product that n the actual job would take. Besides, nearly everything I got from them crapped out - light fittings, LED's. If you try and change it wait another 2 or 3 hours.

  8. #8
    Bronze Member
    Join Date
    Mar 2013
    Location
    Cape Town
    Posts
    111
    Thanks
    0
    Thanked 0 Times in 0 Posts
    I bought remote control downlighters from AC/DC. And installed it for a client, they didn't go white but yellow green and blue. And the remote control is crap for R320 each. I returned it and waited 4 months for feedback and was told there's nothing rong with it. The whole saler amanzimtoti still has my money and AC/DC the downlighters. Stay away from these lights guys

  9. #9
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    there motor control parts are also crap. a direct copy of tele i think. the overload doesnt always fit properly into the contactor.
    even the flameproof parts "warom" they sell is cheap chinese crap.no certification.a copy of ceag. i worked on one where 2 of the 4 terminal screws snapped off with light pressure.

  10. #10
    Diamond Member tec0's Avatar
    Join Date
    Jun 2009
    Location
    South Africa
    Posts
    4,624
    Thanks
    1,884
    Thanked 463 Times in 410 Posts
    Blog Entries
    3
    It doesn't have to be fake, I remember a cranky foreman using glue and a broomstick to glue the breaker so that it couldn't trip. Eventually when someone tried to switched it off they noticed that it was stuck and on fire... The foreman cared more about production then safety. So I would check the cable then the current that it can use and then see what current is running trough it. Secondly I would test the switch and see if it functions.

    As for a fake switch... Yea spotting one without an actual test I would imagine can be tricky...
    peace is a state of mind
    Disclaimer: everything written by me can be considered as fictional.

Page 1 of 2 12 LastLast

Similar Threads

  1. [Question] DIN rail CB's
    By C-Cam in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 20-Jun-12, 07:49 AM
  2. [Question] Circiut Breakers
    By Martinco in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 22-Apr-11, 02:47 PM
  3. Circuit breakers
    By adrianh in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 25-May-10, 12:37 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •