just to blow everything out the water. You cannot use only 1 x 9 kg bottle for a domestic stove as indicated in the table below:


Table 2 ^ Container requirements of typical appliances
1 2 3 4 5
Approximate number of containers
required
Capacity of container
Approximate
input Appliance
22 L (9 kg) 45 L (19 kg)a 113 L (48 kg) kJ/h
Gas stove, normal domestic 1,50 0,65 0,32 42 000

Gas stove, large domestic 2,25 1,00 0,50 63 000
Hotplate (2 burner) 1,00 0,25 0,12 16 000
Instantaneous water heater, multipoint 4,60 2,00 1,00 74 000
Instantaneous water heater, single point 2,00 0,84 0,42 37 000
Gaslight 0,10 0,04 0,02 2 000
Gas iron 0,20 0,08 0,04 3 000
Refrigerator 0,10 0,04 0,02 2 000
Space heater, large, with flue 2,00 0,84 0,42 37 000
Space heater, small, portable type 0,40 0,16 0,08 5 000
NOTE 1 The container requirements may be scaled down if it is unlikely that all appliances will be used
simultaneously for long periods of time.
NOTE 2 This table is based on results that are typical for cold-winter conditions in South Africa; in
warmer conditions the requirements will be less. With experience, a registered installer will learn how
the values can be modified to suit local conditions.
a
It has been found in practice that the approximations given for 45 L (19 kg) containers can usually
also be used for 34 L (13/14 kg) containers.
Table 3 ^ Container requirements for an installation
1 2 3 4
Number of containers required Appliance
22 L (9 kg) 45 L (19 kg) 113 L (48 kg)
Gas stove, normal domestic 1,50 0,65 0,32
Instantaneous water heater, single point 2,00 0,84 0,42
Refrigerator 0,10 0,04 0,02
Gaslights (8 × value given in table 2) 0,80 0,32 0,16
Total number of containers 4,40 1,85 0,9