    Feb 2012
    Got a problem with a 3 phase voltage machine using 2 compressors for heating. When the isolator is in the open position - that is off :-) I get the normal phase to phase voltage of 400V. As soon as I switch the isolator on the machine's phase failure prevents the machine from turning on as the voltage is not the same across the phases. When I measure I get 500 on one then 270 on another. These are really weird voltages I'm getting. I have swapped the phase conductors around which did not help. Could the phase failure be faulty? Any help would be awesome!
    If you're getting 500v across 2 of the phases and only 270 across another two then it sounds like you're missing a phase.
    Test from each phase to an earth at the supply side of the isolator with it in the off position you should get 220-230volts. Disconnect the load and repeat the test on the load side of the isolator with it switched on, you should get the same results.
    Be aware if you're using a digital tester you might get odd readings on the missing phase due to induced or capacitively coupled voltages.
    Gold Member Sparks's Avatar
    Dec 2009
    Few years ago I came acrross an old 2ph+N supply. Even the Boss man at the monkeypality was surprised. Very old supply which was never changed as the property stayed in the family all the years.
    Feb 2012
    Hi Guys thanks for the replies...nice to know there are fellow sparkies out there who are prepared to share their knowledge and experience! It was a the problem was with the neutral not being connected to the correct neutral bar. The machine was connected to a really old Panel with some "shockingly" bad labelling but eventually found the correct bar and bobs your uncle.
    Thanks for letting us know BlueArc, it's always great to get the ending to the story and I'm happy to hear it was something relatively simple and easily fixable.
  1. [Question] Three phase / Single phase
    Last Post: 14-May-12, 10:57 PM
  2. Help please - voltage drop
    By Gei in forum Electrical Contracting Industry Forum
    Last Post: 21-Jan-12, 09:26 AM
  3. Touch Voltage
    By shuudeni in forum Electrical Contracting Industry Forum
    Last Post: 10-Feb-11, 05:46 PM
  4. Difference between: Power factor correction, Voltage regulation and Voltage stabisizi
    By BigRed in forum Electrical Contracting Industry Forum
    Last Post: 08-Feb-10, 09:29 PM