    Earth leakage trip 7 min past the hour every hour

    Earth leakage trip 7 min past the hour every hour. How do I locate the problem? This started after I replaced the old Earth leakage. Driving me mad. The problem is on one of about 7 circuit breakers or combination of them. This tends to happen only at night, but does happen here and there during day hours.
    ~Expenses will eat you alive! - My first Boss~

  2. #2
    Gold Member Chrisjan B's Avatar
    Join Date
    Dec 2007
    Location
    GEORGE
    Posts
    610
    Thanks
    240
    Thanked 72 Times in 65 Posts
    Maybe disable the timer switch....

    Meant as a joke, but it seems there may be sense in the madness?
    Last edited by Chrisjan B; 02-Jan-13 at 01:37 PM. Reason: Added 2nd line...

    BOVER Technologies
    - computer sales and TeamViewer support
    Elmine Botha Freelance Photographer - Photographer/ Videographer

  3. #3
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Do you have any surge protection plugs?

  4. #4
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    If your geyser is fed via the ELCB, remove it. Just make sure it has good earthing because this could be the beginning of the end of your element.

  5. #5
    Email problem IMHO's Avatar
    Join Date
    Jan 2012
    Location
    NW
    Posts
    540
    Thanks
    11
    Thanked 54 Times in 48 Posts
    The geysers have no effect on the tripping of the ELCB. Neither the lights. Just the plugs. It seems to be random, or building up something, that makes it trip in exactly 60 min at night! Exactly 7 min past the hour!
    ~Expenses will eat you alive! - My first Boss~

  6. #6
    Email problem IMHO's Avatar
    Join Date
    Jan 2012
    Location
    NW
    Posts
    540
    Thanks
    11
    Thanked 54 Times in 48 Posts
    I had this problem about a year ago. In the end, I have put the old earth leakage unit back. I forgot about it and replaced it now again. So this condition is around for a long time now. Only timer around, is the one at the pool pump.

    Why would it be hourly at night and only once or twice during the day?
    ~Expenses will eat you alive! - My first Boss~

  7. #7
    New Member
    Join Date
    Jan 2013
    Location
    Rustenburg
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi there! if your ELCB trips every 1hour 7min, then switch your CB's off - one by one for 2-3 hours each.
    This will take long but will eventually locate your culprit.

  8. #8
    Email problem IMHO's Avatar
    Join Date
    Jan 2012
    Location
    NW
    Posts
    540
    Thanks
    11
    Thanked 54 Times in 48 Posts
    Quote Originally Posted by SihleN View Post
    Hi there! if your ELCB trips every 1hour 7min, then switch your CB's off - one by one for 2-3 hours each.
    This will take long but will eventually locate your culprit.
    This is what I am doing. What makes it difficult, I cannot do it during the day, as I can leave all the ELB's on during the day and nothing will trip. I left everything on today again, the whole day and had my first trip at 18h07.

    I have figured out, it is at night, with 6 breakers switched off, that I do not get trip's. However, if I go on any combination, smaller than these 6, I get trips.

    Yes, it is a CBI. But it is the second brand new one. The first was a 63amp 3ka, the second new one is 63amp 6ka.

    I am still testing....
    ~Expenses will eat you alive! - My first Boss~

  9. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    If you have had lightning or power surges recently, the caps could be faulty, you reset and there is no problem, but it will normally just trip randomly, not ever hour, but you never know, i have seen stranger thing happen.

  10. #10
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    It wouldnt be a CBI earth leakage unit by any chance?

Page 1 of 4 123 ... LastLast

Similar Threads

  1. The 4-Hour Work Week
    By derekjay in forum Book Forum
    Replies: 2
    Last Post: 16-Jul-10, 10:33 AM
  2. Charges per hour for electronics?
    By garthu in forum General Chat Forum
    Replies: 2
    Last Post: 19-Apr-09, 04:09 PM
  3. Earth hour
    By Dave A in forum General Chat Forum
    Replies: 38
    Last Post: 04-Apr-09, 11:38 AM
  4. Design a website in under an hour
    By duncan drennan in forum General Business Forum
    Replies: 0
    Last Post: 28-Aug-07, 02:49 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •