    Just to stir things up a bit, how many electricians attach an in line fuse to a 12 volt lamp fitting (between transformer and lamp), I once had to do this to an entire shopping mall.
    Apparently there is nothing that cannot happen today.

  2. #32
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by Slow Blow View Post
    Just to stir things up a bit, how many electricians attach an in line fuse to a 12 volt lamp fitting (between transformer and lamp), I once had to do this to an entire shopping mall.
    Kindly expand on this story so that we can have an idea of the circuitry
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. #33
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I'm guessing it was because the transformers that were installed had no fuse on the secondary side like they're supposed to.
    _______________________________________________

    _______________________________________________

  4. #34
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    398
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Quote Originally Posted by AndyD View Post
    I'm guessing it was because the transformers that were installed had no fuse on the secondary side like they're supposed to.
    Andy as far as I am aware a 50 va transformer does not need a fuse.

    7.9.3.2.4 Secondary overcurrent protection is not required where the
    maximum output of the SELV transformer is 50 VA, the secondary circuit
    conductor is at least 1,5 mm2, not exceeding a length of 2,5 m, and at
    least one conductor and its terminals are insulated to prevent a short
    circuit.

    However, multiple circuits that are fed from a larger transformer must have overload protection on the secondary cables to protect the cable.
    As an example: A 300VA transformer supplies 6 x 50 VA light fittings each supplied by a 1.5mm cable, 2 meters long.
    One light draws 4.2 amps
    Each cable must be protected via a 10 amp circuit breaker in order to protect the cable during a short circuit.
    One common 10amp circuit breaker can be used to protect all the cables but this will be impractical as it will trip under load.
    The transformer and circuit breakers must be housed in a ventilated box and all cable glanded individually.
    See 7.9.3.2.2

    It just seems a lot easier for each light to have it own transformer.

    Additionally, the 50 VA transformer housing can not be used as a junction box, or a looping box, unless it is designed to used as such, which they are not.
    A 3 way looping box must be used on the supply cable and a single cable feed into the transformer.

    This is the correct way to install low voltage lighting
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  5. #35
    Full Member
    Join Date
    Feb 2014
    Location
    Fish Hoek
    Posts
    55
    Thanks
    6
    Thanked 3 Times in 3 Posts
    Quote Originally Posted by Leecatt View Post
    Andy as far as I am aware a 50 va transformer does not need a fuse.

    7.9.3.2.4 Secondary overcurrent protection is not required where the
    maximum output of the SELV transformer is 50 VA, the secondary circuit
    conductor is at least 1,5 mm2, not exceeding a length of 2,5 m, and at
    least one conductor and its terminals are insulated to prevent a short
    circuit.

    However, multiple circuits that are fed from a larger transformer must have overload protection on the secondary cables to protect the cable.
    As an example: A 300VA transformer supplies 6 x 50 VA light fittings each supplied by a 1.5mm cable, 2 meters long.
    One light draws 4.2 amps
    Each cable must be protected via a 10 amp circuit breaker in order to protect the cable during a short circuit.
    One common 10amp circuit breaker can be used to protect all the cables but this will be impractical as it will trip under load.
    The transformer and circuit breakers must be housed in a ventilated box and all cable glanded individually.
    See 7.9.3.2.2

    It just seems a lot easier for each light to have it own transformer.

    Additionally, the 50 VA transformer housing can not be used as a junction box, or a looping box, unless it is designed to used as such, which they are not.
    A 3 way looping box must be used on the supply cable and a single cable feed into the transformer.

    This is the correct way to install low voltage lighting
    Leecatt is correct, but, The Western Cape Approved Electrical Inspection Authority has made the local rule of having to put an in line 10 amp fuse between even a 50w transformer and the lamp, so I just do it anyway to avoid any legal complications in the event of an accident.
    I don't know if this is approved by, err, who approves things electrical nowadays
    Apparently there is nothing that cannot happen today.

Page 4 of 4 FirstFirst ... 234

Similar Threads

  1. Installation of 220V downlights
    By Oblivious in forum Electrical Contracting Industry Forum
    Replies: 105
    Last Post: 14-Feb-20, 09:57 AM
  2. Down lights, 220v lamps in 12 volt fittings?
    By billybob2475 in forum Electrical Contracting Industry Forum
    Replies: 14
    Last Post: 10-Jun-11, 10:18 AM
  3. A Erwin on compact fluorescent lamps rollout programme
    By I Robot in forum Electrical Load Shedding Forum
    Replies: 4
    Last Post: 05-Sep-08, 06:13 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •