    Is there a chart or table that can help me determine the acceptable loop impedance and PSU results on an existing installation.

  2. #2
    Email problem
    Join Date
    Apr 2012
    Location
    Sandton
    Posts
    9
    Thanks
    0
    Thanked 1 Time in 1 Post
    From SANS 10142-7 : 8.7.5, At the main switch, the impedance shall be such that an earth fault current double the rated current (or higher) of the main protective device automatically disconnects the supply to the installation. The formula
    for a 60 amp supply : voltage over 2 x current ( V/2I ) ie 230 divided by 120 = 1.92ohms. A reading less than 1.92ohms is acceptable. (p.s. post again if you need this test described in laymans terms)
    Your second question - I presume you mean PSC (prospective short circuit)(rating). What is the rating of your breakers?
    Probably 5kA or 5000amps (marked on the breaker) - your reading must be less than that.

  3. Thanks given for this post:

    Dave A (27-Apr-12)

  4. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,403
    Thanks
    513
    Thanked 854 Times in 687 Posts
    Welcome to the forum Mojakoki
    _______________________________________________
    I am special and so is Vanash.
    _______________________________________________

  5. #4
    New Member
    Join Date
    Apr 2012
    Location
    Edenvale JHB
    Posts
    6
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks! I was recently told by the council we can't accept readings above 1.4ohms. Got a bit confused.

    On 3 phase - would I then use 380V or 230V.

  6. #5
    Email problem
    Join Date
    Apr 2012
    Location
    Sandton
    Posts
    9
    Thanks
    0
    Thanked 1 Time in 1 Post
    If your reading is high, (too high for your Council's liking), consider installing an earth rod.
    Pretty sure you would use 230V for a 3 phase installation as you are testing the earth resistance back to the transformer where the suppliers earth is supplied.