Thread: Disconnecting a gate motor

  1. #21
    Full Member
    Join Date
    Feb 2011
    Location
    Scotland
    Posts
    46
    Thanks
    2
    Thanked 5 Times in 4 Posts
    Quote Originally Posted by AndyD View Post
    I have a kit with several different MCB and MCCB lockout devices aswell as colour coded padlocks and signage, there's one on each of our vehicles as well. They don't cost a fortune and they're an HSE requirement on many sites nowadays.

    There are lockout covers you can fit on plugs and padlock to prevent them being plugged in again so a plug can be considered a lockable disconnect if the right device is used.
    Hey Andy where did u buy the locking device for the MCB?

  2. #22
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    heineman/cbi have both the heineman unit and the new clip system...or you can get the one for the din rail mount type breakers from AC/DC...dont forge tto print and laminate a dange rdo not switch on label with your contact details

  3. Thank given for this post:

    Dave A (20-Feb-12), SparkyScott (19-Feb-12)

  4. #23
    New Member
    Join Date
    Feb 2012
    Location
    Johannesburg
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Hi guys

    It is compulsory to have an isolator installed within arm's reach of the gate motor, so that the electrical power can be cut should an emergency situation arise. It is recommended that a 5A thermal breaker with all-pole circuit break is used. Page 14 of this installation manual shows the position of the isolator.

    I hope this helps :-)

  5. #24
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,662
    Thanks
    3,308
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by CharlM View Post
    It is compulsory to have an isolator installed within arm's reach of the gate motor, so that the electrical power can be cut should an emergency situation arise.
    Hi Charl and welcome to the discussion. Could you back that statement up by pointing to the relevant section of code, please.

  6. #25
    New Member
    Join Date
    Feb 2012
    Location
    Johannesburg
    Posts
    3
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Dave A View Post
    Hi Charl and welcome to the discussion. Could you back that statement up by pointing to the relevant section of code, please.
    Sure, it is in the SANS10142-1 manual, section 6.9.3 - Disconnecting devices for equipment Amdt 3

    6.9.3.1 An appliance or equipment that is not supplied from a socket-outlet, including equipment automatically or remote controlled, shall be capable of being disconnected from the supply by an easily accessible switch-disconnector. The disconnector shall be mounted (if not specified elsewhere in this part of SANS 10142, but excluding luminaire circuits) (see also 6.16.1.4) Amdt 1
    a) within arm's reach from the terminals of the appliance, or
    b) in a distribution board, if the device is capable of being locked in the open position

  7. #26
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,662
    Thanks
    3,308
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by CharlM View Post
    Sure, it is in the SANS10142-1 manual, section 6.9.3 - Disconnecting devices for equipment Amdt 3

    6.9.3.1 An appliance or equipment that is not supplied from a socket-outlet, including equipment automatically or remote controlled, shall be capable of being disconnected from the supply by an easily accessible switch-disconnector. The disconnector shall be mounted (if not specified elsewhere in this part of SANS 10142, but excluding luminaire circuits) (see also 6.16.1.4) Amdt 1
    a) within arm's reach from the terminals of the appliance, or
    b) in a distribution board, if the device is capable of being locked in the open position
    I see we have come full circle. This was the starting point of post 1, but with a totally different interpretation.
    Please note the highlighted bits above which are pretty important to the correct interpretation...

    Just in the section you've quoted we've already got a couple of options other than the isolator within arms reach:

    • The appliance is supplied from a socket-outlet - you don't need an isolator within arms reach of the terminals of the appliance (unless specified elsewhere)
    • There is a lockable switch disconnector device in the distribution board - you don't need an isolator within arms reach (unless specified elsewhere)


    The "if not specified elsewhere" bit is touched on in post 9. Section 6.16.5.1 is all about motor protection and control - and 6.16.5.1.5 provides four options, only one of which is a disconnector "mounted on or next to the motor".
    Last edited by Dave A; 20-Feb-12 at 04:25 PM. Reason: typo

  8. #27
    Suspended
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    893
    Thanks
    8
    Thanked 61 Times in 54 Posts
    Quote Originally Posted by CharlM View Post
    Sure, it is in the SANS10142-1 manual, section 6.9.3 - Disconnecting devices for equipment Amdt 3

    6.9.3.1 An appliance or equipment that is not supplied from a socket-outlet, including equipment automatically or remote controlled, shall be capable of being disconnected from the supply by an easily accessible switch-disconnector. The disconnector shall be mounted (if not specified elsewhere in this part of SANS 10142, but excluding luminaire circuits) (see also 6.16.1.4) Amdt 1
    a) within arm's reach from the terminals of the appliance, or
    b) in a distribution board, if the device is capable of being locked in the open position
    This is the way we installers have all been instructed to install gate motors. This is also the way that electricians doing coc's are also calling it - never really had a debate with them so have just gone the route of putting a plugpoint within 1m of the motor.

  9. #28
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,662
    Thanks
    3,308
    Thanked 2,676 Times in 2,258 Posts
    Blog Entries
    12
    Quote Originally Posted by Kevinb View Post
    never really had a debate with them so have just gone the route of putting a plugpoint within 1m of the motor.
    Kevin, there's no harm in that. It's a great way to do it

    It's when people start stating it's "compulsory" - i.e. the only way to do it that the problems start. People start believing it, then sparkies who issue COC's on an installation that is up to code, but deals with this issue a different way, start copping flack because folk have been misinformed.

    It's unnecessary aggravation and I'd prefer to nip it in the bud before the disease spreads.

    The big question that still remains, given Andy's lockable plug-top device option, is whether any plug-top can therefor be considered a lockable disconnector device?

    For the time being I've advised my sparkies not to rely on the idea when examining installations... for no better reason than it would make the line of site to plug point option redundant (and that would still have to be complied with when it comes to motors on plug-tops anyway).

    It's for things like these that a practice note from the regulatory authority would be really useful.
    Last edited by Dave A; 20-Feb-12 at 08:33 PM. Reason: update - clarification

  10. #29
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I think you've hit the nail on the head. From a real world point of view a 16A 3-pin plug (or any other plug) is a device that would easily fulfil the definition of being a safe lock-out device. Sure you need a 'tool' to do it but that's no different than an MCB or MCCB where many brands require their own proprietary toggle clip. I'm guessing that the legislation was written by persons who weren't aware of suitable devices being on the market and I have to say they wouldn't be alone, I'm yet to see anyone else making use of these devices.

    I agree there's no 'harm' in making the plug point within a meter but it's certainly an unnecessary inconvenience in many cases and possibly extra expense. If I was involved in domestic electrical or access systems work it would annoy the hell out of me but as I'm not I refuse to get stressed about it. The ball's in you're court Dave I wish you luck and Godspeed. Let us know how you get on with the appropriate authorities.
    _______________________________________________

    _______________________________________________

  11. #30
    Suspended
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    893
    Thanks
    8
    Thanked 61 Times in 54 Posts
    I get called out quite a lot because someone might be selling a house and they cannot get a coc, because the motor was installed a couple of years ago and does not have a plugpoint within one metre of the gate therefore they cannot get a coc. So this comes from a lot of different sparkies who insist on this to issue the coc.

Page 3 of 7 FirstFirst 12345 ... LastLast

Similar Threads

  1. VAT on motor oil
    By J7J in forum Tax Forum
    Replies: 2
    Last Post: 12-Jan-12, 09:46 PM
  2. Electric Motor or Generator ?
    By daveob in forum Electrical Load Shedding Forum
    Replies: 10
    Last Post: 17-Oct-11, 06:01 PM
  3. disconnecting and reconnecting electricty
    By murdock in forum General Business Forum
    Replies: 18
    Last Post: 04-Mar-11, 03:55 PM
  4. Motor winding insulation
    By mikilianis in forum Electrical Contracting Industry Forum
    Replies: 4