I always installed a contactor and selected "Signal islanding mode" before. Installed a 8kW Sunsynk this week and was surprised to find PE/N
Andrew_van_Zyl Today, 07:07 PMYou dont need to use PV cables between the combiner and the inverter, the PV cables are double insulated for use on the roof.
Just make
Hi guys, does anyone know who stocks 16 and 25mm PV cables? Inverter max capacity is 80A and I will have 68A to connect between combiner box and inverter.
Sparks Today, 12:52 PMThanks Derlyn. I appreciate the input and I may have to do this as I cannot see Eskom rectifying the problem.
RegElec Today, 12:48 PM
Neutral/earth bridging method.
According to SANS neutral and earth may not be bonded after the point of control. After an installation I isolate the grid and take readings and if my
Sparks Today, 07:47 PM