• I Robot

    There is no available content written by I Robot
  • Recent Article Comments

  • Recent Blog Posts

  • Recent Forum Posts

    RegElec

    ELI Way out of Spec

    Noted. I have access to the meter box so I will see whether it can be done there.

    RegElec Today, 11:22 AM Go to last post
    GCE

    ELI Way out of Spec

    I would rather have done it at the meter box if possible at least then i would not have contravened 6.1.6 and if there is a huge surge down neutral earth

    GCE Today, 10:46 AM Go to last post
    RegElec

    ELI Way out of Spec

    Thanks for the replies. The comments are as expected. I have bridged the earth / neutral in the main DB and left the sub DB's as TN-S. We will just have

    RegElec Today, 10:23 AM Go to last post
    Dave A

    ELI Way out of Spec

    I wonder how widespread that problem is nowadays.

    Dave A Today, 07:23 AM Go to last post
    GCE

    ELI Way out of Spec

    I Agree with Derlyn

    Further to that and a problem that could occur by earthing the earth neutral - How big is the pole top transformer ,

    GCE Today, 06:40 AM Go to last post