    Derlyn

    Neutral/earth bridging method.

    7.16.4.5 makes it illegal to supply an inverter through an ELU on it's input side.


    7.16.4.5 The neutral shall not be earthed beyond

    Derlyn Today, 12:26 PM Go to last post
    Isetech

    Neutral/earth bridging method.

    The comment about the ELU has nothing to do with the contactor/relay, if you do a permanent bond and fit an ELU on the input side of the inverter it will

    Isetech Today, 11:21 AM Go to last post
    GCE

    PV Suppliers?

    Most burnt connections etc I have seen are bad workmanship , strands cut off before fitting into lugs , AC equipment used in place of DC , DC CB used

    GCE Today, 10:31 AM Go to last post
    GCE

    Neutral/earth bridging method.

    If the contactor is correctly sized for the neutral earth bond the chances of failure are extremely low - the same way that if a CB is sized correctly

    GCE Today, 10:26 AM Go to last post
    GCE

    Solar challenges

    Would be interested to know what the demands where made and what you deem not be in contravention

    GCE Today, 10:11 AM Go to last post