The comment about the ELU has nothing to do with the contactor/relay, if you do a permanent bond and fit an ELU on the input side of the inverter it will
Isetech Today, 11:21 AMMost burnt connections etc I have seen are bad workmanship , strands cut off before fitting into lugs , AC equipment used in place of DC , DC CB used
GCE Today, 10:31 AMIf the contactor is correctly sized for the neutral earth bond the chances of failure are extremely low - the same way that if a CB is sized correctly
GCE Today, 10:26 AMWould be interested to know what the demands where made and what you deem not be in contravention
GCE Today, 10:11 AM
Neutral/earth bridging method.
7.16.4.5 makes it illegal to supply an inverter through an ELU on it's input side.
Derlyn Today, 12:26 PM7.16.4.5 The neutral shall not be earthed beyond