Thread: Sockets outlets installed behind appliances

  1. #1
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts

    Sockets outlets installed behind appliances

    A common practise is to mount the socket outlet under the counter behind the appliance ... I regard this as extremely dangerous ... hence the reason I always fit the socket outlet for an appliance above the counter or next to the appliance ... would it be marked a fail on an inspection report ?


    "6.16.1.2 The power supply to every fixed appliance, except luminaires, shall
    be supplied through
    a) a disconnecting device that disconnects both live conductors in a singlephase supply and all phase conductors in a multiphase supply, or
    b) a socket-outlet that is directly accessible at all times that any person is
    exposed to such appliance while the supply is on. In the case of a remotely
    installed appliance, the position of the disconnecting device shall be
    indicated by means of a notice in close proximity to or on the appliance. "
    Comments are based on opinion...not always facts....that's why people use an alias.

  2. #2
    Silver Member
    Join Date
    Jul 2008
    Location
    Germiston, South Africa
    Posts
    397
    Thanks
    24
    Thanked 47 Times in 43 Posts
    Would an under counter washing machine or tumble drier, for example, be regarded as a "fixed appliance"?

    Sent from my SM-A705FN using Tapatalk
    To make a mistake is human, to learn from that mistake is knowledge and knowledge is strength.

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    761
    Thanks
    119
    Thanked 35 Times in 34 Posts
    If that's the case then perhaps an isolator to said sockets which are behind the washing machine under the counter?

    Sent from my SM-N960F using Tapatalk

  4. #4
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Leecatt View Post
    Would an under counter washing machine or tumble drier, for example, be regarded as a "fixed appliance"?

    Sent from my SM-A705FN using Tapatalk
    Another interesting topic ... if the machine is free standing and without a counter top it s free standing machine with access to the switch ...however as soon as you push the machine under a counter with the sides closed ... how do you access the plug top to switch off the device ... it now becomes a dangerous situation with no means to get to the switch without going to the DB and shutting down the power ... unless of course you know which circuit it is ( because it would have suitable label indicting which circuit ... if we going to go down that road we could ask the question why is an a fixed appliance if you dont screw it to the cupboard and leave it free to remove ... but some will apply a little common sense.

    What I generally do is fit a flush mount double pole isolator above the counter the pull the cable into the isolator which then makes it a fixed appliance ... not all customer want it dont like this because it means having to call you back to disconnect the ideal method would be to fit a 4x3 single socket under the counter and a double pole isolator above the counter.
    From my experience ... generally what happens ... the customer experiences a tingling feel or the plug tops is burnt due to a loose connection in solid plug tops (come with the machine) or socket outlet or a more common one now is the hollow 2 amp plug being sold and fitted to tumble driers and washing machines ... or someone has disconnected the earth from the plug top because it trips the earth leakage.
    Comments are based on opinion...not always facts....that's why people use an alias.

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Dylboy View Post
    If that's the case then perhaps an isolator to said sockets which are behind the washing machine under the counter?

    Sent from my SM-N960F using Tapatalk
    yip that would be ideal.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,248
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi

    The definition of fixed appliance needs to be taken into account

    3.3.3
    fixed appliance
    appliance that is fastened or otherwise secured at a specific location, and
    that would require the use of tools to be moved to another location


    I would not put a wash machine , microwave etc as a fixed appliance , I would class it as a stationary appliance
    When in doubt with regulations I generally go look in definitions to check for clarity

    3.3.4
    portable appliance
    appliance that is moved in the course of normal operation
    3.3.5
    stationary appliance
    appliance that is normally not moved or cannot easily be moved while in
    operation

  7. Thanks given for this post:

    Dave A (04-Dec-21)

  8. #7
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    225
    Thanks
    11
    Thanked 21 Times in 19 Posts
    Think of gas stove, plugging in or the double dour fridge at corner store both plugs 300 mm from ground. I want to see you switch that off or unplug it..

  9. #8
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Thys LOW Elektries View Post
    Think of gas stove, plugging in or the double dour fridge at corner store both plugs 300 mm from ground. I want to see you switch that off or unplug it..
    I dont think you should have a plug behind a gas stove

    https://thegasman.co.za/pages/lp-gas-regulations
    Comments are based on opinion...not always facts....that's why people use an alias.

  10. #9
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I am getting distracted now ... My homework this weekend is suppose to be 7.12 alternative suppliers ... reading ed 3 ... now I have to download ed 3.1 and find NRS 097 .. .to much for my little brain and the weekend has only just begun.
    Comments are based on opinion...not always facts....that's why people use an alias.

Similar Threads

  1. [Question] New inverter aircon installed and ELCB bypassed
    By Viksharma in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 12-Apr-21, 08:22 PM
  2. [Question] Link installed Pastel help so that F1 will work
    By michellepace in forum Accounting Forum
    Replies: 2
    Last Post: 03-Feb-20, 10:04 AM
  3. switched socket outlets or not!
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 18-Aug-16, 11:16 PM
  4. [Question] Can plumbing pipes (copper etc) be installed next to and behind my DB & across my conduit?
    By ACEsterhuizen in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 22-Jan-16, 09:15 AM
  5. Generator installed before council meter
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 12-Nov-15, 06:18 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •