Thread: Earth Leakage Breaker (RCD) Tripping

  1. #31
    New Member
    Join Date
    Oct 2017
    Location
    Uitenhage
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks for that info AndyD, very informative (even 5 years later). I have a question though, is there a limit on how many milliseconds the RCD should take to trip? I did a check across 37 installed RCD's and the time range from 9 to 203 milliseconds.

  2. #32
    New Member
    Join Date
    Oct 2017
    Location
    Uitenhage
    Posts
    5
    Thanks
    0
    Thanked 0 Times in 0 Posts
    I found a document, VC8035 From 1987, Compulsory Specification for Earth leakage protection units.

    It lists the following times:

    Click image for larger version. 

Name:	elu time.jpg 
Views:	246 
Size:	92.8 KB 
ID:	7931

    Are they still relevant?

  3. #33
    New Member
    Join Date
    Jul 2023
    Location
    Cape Town
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by AndyD View Post
    If there's anything I missed, anything that's inaccurate or anything that doesn't read too well grammatically please let me know.
    Andy - that was an amazing summary that prompted me to sign up and congratulate you.
    This is my first ever post.
    And also to ask a question which I hope is not deemed too dumb.
    How many circuit breakers can one connect on a bank supplied by a single RCB/EL?
    Is there a limit or does one break it up for easier management in future fault-finding?
    The DBs I have seen mostly have only the plug circuits on EL. Typically 20A C/Bs.
    eg - I have seen DBs with 10x20A C/Bs on a single EL. Others with max of 5x20A C/Bs on EL and with 2 or 3 "banks" of these.
    Most are "old style" black Samite but some are "new style" DIN rail.
    Thx
    C

  4. #34
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by MCP View Post
    Andy - that was an amazing summary that prompted me to sign up and congratulate you.
    This is my first ever post.
    And also to ask a question which I hope is not deemed too dumb.
    How many circuit breakers can one connect on a bank supplied by a single RCB/EL?
    Is there a limit or does one break it up for easier management in future fault-finding?
    The DBs I have seen mostly have only the plug circuits on EL. Typically 20A C/Bs.
    eg - I have seen DBs with 10x20A C/Bs on a single EL. Others with max of 5x20A C/Bs on EL and with 2 or 3 "banks" of these.
    Most are "old style" black Samite but some are "new style" DIN rail.
    Thx
    C
    Per regulations you can put as many CB after the Earth leakage as you want to - The Earth leakage has to be overloaded protected so in a domestic situation usually 63Amp isolator type earth leakage an it would have a max of 63Amp CB protecting.

    Good practice is to install limited CB after the earth leakage and that is very dependent on usage - Every appliance has a leakage to earth so eventually an earth leakage will trip purely due to the qty of appliances leaking to earth , some worse than others

    In smaller house you would do 1 ELU and 3 plug circuits , In a bigger house maybe 2 earth leakages or 3

    My previous house I had 5 Earth Leakage units , where I squat now I have 3 and really only need 1 but I don't like struggling when I get home , I prefer drinking a beer in peace

Page 4 of 4 FirstFirst ... 234

Similar Threads

  1. Does a stove need to be on an earth leakage?
    By Leecatt in forum Electrical Contracting Industry Forum
    Replies: 63
    Last Post: 23-Jan-18, 08:26 AM
  2. [Question] Earth Leakage Confusion
    By ursi in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 09-Nov-15, 08:44 PM
  3. Earth leakage tripping when plug in snake rack
    By MattyN in forum Electrical Contracting Industry Forum
    Replies: 7
    Last Post: 22-Aug-15, 09:29 AM
  4. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM
  5. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM

Tags for this Thread

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •