    Socket outlet above hob

    What do you do when you find a socket outlet this close above a hob in an existing installation?
    Is it compliant for the issue of a 9.2 (b) electrical COC?

    Click image for larger version. 

Name:	socket outlet location.jpg 
Views:	1169 
Size:	37.2 KB 
ID:	7301

    As a guide, I always look at the full code. So some food for thought on this -

    Noting the position of the stove isolator, 6.16.3.1.2 c) states that the switch-disconnector should preferably not be above the cooking appliance.

    6.15.6.1 states that a socket outlet that is exposed to the weather (or to the condensation, dripping, splashing or accumulation of water) shall have a rating of at least IP44 in accordance with...

  2. Thanks given for this post:

    Ishmaelmo (14-Nov-18)

  3. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi Dave

    Questions as above are good reminders as to why I don't get involved in your market.

    My feeling is that if you are going to issue under 9.2(b ) then it needs to comply to fundamentals - I would struggle to pass it under 5.3.8 , pasted below.
    If there are pots on the stove boiling water the socket outlet will not be readily accessible for normal operation .

    I would look at blanking the socket off and run in a new socket outlet for what ever is plugged in there at the moment

    5.3.8 Positioning and accessibility of electrical equipment
    Electrical equipment shall be so positioned that
    a) it does not impair the functioning or safety of other equipment,
    b) it is readily accessible for installation, replacement, operation, testing,
    inspection, maintenance and repair (see 6.6.1.9 and 6.9.4 for the main
    switch). All parts of the installation shall be accessible without the need to
    enter any adjoining premises (for example, in an apartment building),
    NOTE Common areas (such as passages and entrance halls) are not regarded
    as adjoining areas.
    c) there is easy access to its location,
    d) it is not likely to be physically damaged,
    e) dust or moisture is not likely to accumulate on live or other parts and
    cause flashover, and
    f) where the distribution board is concealed by a cupboard or other
    covering, the notice for live electrical apparatus referred to in annex N
    shall be in a conspicuous place indicating the position of the distribution
    board.

  4. Thanks given for this post:

    Ishmaelmo (14-Nov-18)

  5. #3
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I'd fail that particular socket and isolator citing the 5.3.8 reg above regarding liklihood of physical damage (due to heat) and moisture likely to accumulate, it's within 200mm of a red hot hob element and probably less than 100mm from the top of an average sized boiling pot and any trailing cables plugged into that socket would hang even closer
    _______________________________________________

    _______________________________________________

Similar Threads

  1. socket-outlet question
    By Hotspot in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 28-Aug-16, 03:06 PM
  2. Socket Outlet Confusion
    By BlueArc in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 05-Nov-14, 11:57 AM
  3. [Question] Socket Outlet positionings
    By Smut in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 06-Mar-14, 01:33 PM
  4. unknown socket outlet
    By pipewood in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 09-Nov-12, 06:38 PM
  5. Socket outlet in bathroom
    By mlpotgieter in forum Electrical Contracting Industry Forum
    Replies: 11
    Last Post: 23-Oct-11, 12:10 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •