    Quote Originally Posted by ians View Post
    ...they didnt think to add the round 2 pin...the one that all electrical power tools are supplied and some of my kitchen appliances.
    The Schuko socket?

    Quote Originally Posted by ians View Post
    yip.
    Now there's another fine can of worms.

    No Schuko plug or socket or may be imported or sold in SA (see page 4 of the attached Government Notice where it has been specifically declared illegal), but as you say, no shortage of them about.

    VC 8008 (2010).pdf

    For those not familiar with the Schuko outlet -

    Click image for larger version. 

Name:	schuko outlet.jpg 
Views:	448 
Size:	10.2 KB 
ID:	7128

  2. Thanks given for this post:

    AndyD (08-Jun-18)

  3. #12
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,924
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Is that your bathroom Dave? As the estate agents say...location, location, location and that's certainly a lovely location for that socket, I can only assume there's a nice big 20Amp isolating transformer behind it. Nice to see it covers all bases and even the illegal ones with equal aplomb, there's even a cunning little ledge under it giving you somewhere to balance your hairdryer above the full basin. Certainly goes above and beyond, full marks from me.
    _______________________________________________

    _______________________________________________

  4. #13
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,659
    Thanks
    3,307
    Thanked 2,678 Times in 2,259 Posts
    Blog Entries
    12
    Quote Originally Posted by AndyD View Post
    As the estate agents say...location, location, location and that's certainly a lovely location for that socket, I can only assume there's a nice big 20Amp isolating transformer behind it.
    It was actually the query about the location we posed to the ECA technical advisory staff that "induced" the point about the Schuko socket & outlet ban.

  5. #14
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Hi Dave

    Do you still have the answer handy with regards to the location of the socket and proximity of the basin ( let's forget about the illegal schuko)

    My understanding would be if the bath or shower basin is far enough away from the socket outlet , being 600mm ( Zone 2) , then the socket outlet would be allowed above the basin/tap.
    Socket outlets on Earth leakage unit are allowed in zone 3

    There are no zones around a hand basin and tap the way I read the regulations.

  6. #15
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,659
    Thanks
    3,307
    Thanked 2,678 Times in 2,259 Posts
    Blog Entries
    12
    Quote Originally Posted by GCE View Post
    There are no zones around a hand basin and tap the way I read the regulations.
    Correct. Not in SA anyway.
    Madness, I reckon.

  7. Thanks given for this post:

    GCE (22-Jun-18)

  8. #16
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by Dave A View Post
    Correct. Not in SA anyway.
    Madness, I reckon.
    Common sense would be the logical answer...but as you mentioned...not in SA

  9. #17
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    I thought i would do some scratching...

    The unearthed schuko plugs falls under SANS 164-6

    2 pole systems, 16A 250 Vac for connection of class 2 equipment.

    MCE sell them and advertise on the front page of the sparks mag.


    Quote Originally Posted by Dave A View Post
    The Schuko socket?


    Now there's another fine can of worms.

    No Schuko plug or socket or may be imported or sold in SA (see page 4 of the attached Government Notice where it has been specifically declared illegal), but as you say, no shortage of them about.

    VC 8008 (2010).pdf

    For those not familiar with the Schuko outlet -

    Click image for larger version. 

Name:	schuko outlet.jpg 
Views:	448 
Size:	10.2 KB 
ID:	7128

  10. #18
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,659
    Thanks
    3,307
    Thanked 2,678 Times in 2,259 Posts
    Blog Entries
    12
    And then you get the ones installed in the Vodacom charging kiosk in the domestic departure area at O.R. Tambo International Airport.

    Click image for larger version. 

Name:	20180613_144141.jpg 
Views:	269 
Size:	43.3 KB 
ID:	7162

    Click image for larger version. 

Name:	20180613_144023.jpg 
Views:	283 
Size:	49.4 KB 
ID:	7164

    Click image for larger version. 

Name:	20180613_144023.jpg 
Views:	308 
Size:	55.8 KB 
ID:	7163

    As you say, apparently the issue of concern is the exposed earth contact points. It did make me wonder about the wisdom of allowing bare copper wiring and strapping for earthing and bonding...

    Perhaps that is why the ban comes via Department of Trade and Industry

  11. #19
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,246
    Thanks
    34
    Thanked 304 Times in 258 Posts
    The main reason for the ban - If there is an earth fault ( small so as not to trip ) or the fault occurs while unplugging - The live pin could still be connected to the socket outlet while the earth has disconnected and you could be holding the earth strap on the side of the plug top effectively becoming the earth.
    There is talk in Europe of having a re look at the schuko - Some of the countries have already stopped the use thereof

  12. Thanks given for this post:

    Dave A (03-Jul-18)

Page 2 of 2 FirstFirst 12

Similar Threads

  1. [Question] SANS 10400 XA
    By Les Abbott in forum Energy and Resource Conservation Forum
    Replies: 0
    Last Post: 01-Jun-17, 01:20 PM
  2. SANS Regulations
    By AndyD in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 26-Sep-15, 10:09 AM
  3. sans 724 and sans 984
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 31-Jul-10, 04:35 PM
  4. SANS codes.
    By I Robot in forum Electrical Contracting Industry Forum
    Replies: 48
    Last Post: 09-Apr-10, 07:52 AM
  5. sans junction box
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 20-Mar-10, 10:13 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •