Thread: Understanding Earth Leakage

  1. #1
    New Member
    Join Date
    Sep 2020
    Location
    Cape Town
    Posts
    3
    Thanks
    2
    Thanked 0 Times in 0 Posts

    Understanding Earth Leakage

    Long story short: I had a disaster of a building experience, including shoddy electrical workmanship. In the process of arranging proper CoC but there are a few things I want to understand around earth leakage.

    On my DB I have two neutral connection bars, one comes straight from mains and other is sourced from the neutral from earth leakage (EL). Due to one of the electricians mislabeling the circuits everything was a mess, meaning that neutral was being taken from incorrect places for things like my geyser and pool pump.

    Both my geyser and pool pump's neutral was coming from the non-EL neutral bar which caused the EL to trip. After them being moved to the EL neutral bar there's been no tripping. For my own education I'd like to understand why:

    1. Did the pool pump and geyser cause EL to trip? Is it because L was coming from the EL but N was not?
    2. It seems like my light circuits are coming from non-EL neutral bar - why not just put everything on EL? Is there a good reason to not connect it via EL?
    3. For something like a pool pump, would it make more sense to have both L and N coming directly from the mains and then have a earth leakage at the pool pump's db?

    Sorry if my weak attempt at terminology is hard to follow...

  2. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    In essence the earth leakage unit ensures that the current being supplied on the live terminal is matched by the current returning via the neutral terminal.

    This means that for every circuit where the live that is supplied via the ELU, the associated neutral will have to be connected to the ELU's neutral bar.
    If a circuit has the live supplied before the ELU, but the neutral returning through the ELU, any current through the circuit will result in an imbalance at the ELU and the ELU will trip.
    Same problem when the live is supplied after the ELU but the neutral is connected to the neutral bar before the ELU.

    Quote Originally Posted by saguy View Post
    2. It seems like my light circuits are coming from non-EL neutral bar - why not just put everything on EL? Is there a good reason to not connect it via EL?
    I have everything on ELU protection at my house and it isn't a problem. The "benefit" of not putting a circuit on ELU protection is one does not get "nuisance tripping" for accumulated small current losses to earth or temporary imbalances that may occur when a load is switched on or a light point gets wet. Please note that some types of circuits must be on earth leakage protection.

    Quote Originally Posted by saguy View Post
    3. For something like a pool pump, would it make more sense to have both L and N coming directly from the mains and then have a earth leakage at the pool pump's db?
    The benefit of doing it this way is that if there is a fault at the pool pump that causes the ELU to trip, it would only affect the pool pump and not the rest of the installation.

  3. Thanks given for this post:

    saguy (04-Jun-21)

  4. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Quote Originally Posted by saguy View Post
    3. For something like a pool pump, would it make more sense to have both L and N coming directly from the mains and then have a earth leakage at the pool pump's db?
    .
    Yes. It does make more sense.
    When I design the circuitry for an installation, I make sure that each sub DB has it's own earth leakage relay.
    Supply cables to sub db's not on earth leakage.

    Makes fault finding a lot easier and as Dave mentioned, should there be an earth fault then the whole installation is not affected.

    Also if possible, keep lighting off earth leakage. Should there be an earth leakage fault at night, at least you will have lights.

    Peace out ... Derek.

  5. Thanks given for this post:

    saguy (04-Jun-21)

  6. #4
    New Member
    Join Date
    Sep 2020
    Location
    Cape Town
    Posts
    3
    Thanks
    2
    Thanked 0 Times in 0 Posts
    Thank you both, that clears things up a lot.

    Is there any way to actually test at a plug point or light fixture that the L and N are connected correctly to L and N (either both on ELU or both not).

  7. #5
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The cheap and cheerful socket testers you can buy at Macro or Builders Warehouse can give you an indication that the socket is connected right and whether it's on an earth leakage circuit. I don't think there's any DIY type testers that will check lighting points.
    _______________________________________________

    _______________________________________________

  8. #6
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by AndyD View Post
    The cheap and cheerful socket testers you can buy at Macro or Builders Warehouse can give you an indication that the socket is connected right and whether it's on an earth leakage circuit. I don't think there's any DIY type testers that will check lighting points.
    A globe
    Comments are based on opinion...not always facts....that's why people use an alias.

  9. #7
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    224
    Thanks
    11
    Thanked 21 Times in 19 Posts
    A globe is good but what about a plug on a E27 fitting?
    https://www.acdc.co.za/products/e27-...nt=41237504140
    If you put a yanis adaptor on the lead one can test the lights? Can it work or not?

  10. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Yes, you could make that E27 adaptor cable thingy into a test lead to check supply voltage and supply polarity. It just wouldn't be able to give you an earth loop Zs reading. You could splash out on one of these as well and it would work for bayonett fittings https://www.acdc.co.za/pages/product-individual?LHA-01 and for E14 fittings https://www.acdc.co.za/pages/product-individual?LHA-07 and even GU 10 https://www.acdc.co.za/pages/product-individual?LHA-10
    _______________________________________________

    _______________________________________________

Similar Threads

  1. Earth Leakage
    By Gtfast in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 10-May-16, 10:11 PM
  2. Earth leakage
    By Electrix in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-16, 09:10 PM
  3. [Question] Inverter's and earth leakage
    By padayad28 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 11-Jul-15, 09:08 AM
  4. earth leakage tripping
    By ians in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 23-Jun-15, 11:27 AM
  5. Earth Leakage
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 13
    Last Post: 27-May-13, 12:03 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •