    35A change over switch.

    Had to do a generator installation during the week so off I went in search of a change over switch.

    At the one wholesaler they had 2 on offer, both MCE brand.
    The one, 35A and the other 63A.

    I enquired: Who buys a 35A change over switch ?
    Answer: The guys who install small generators.

    I chuckled and explained to the young lad that when the generator is not in use, the total current drawn by the installation
    is still going through the switch, which on a single phase domestic installation can be up to 60A.

    It took me quite a while to convince him.

    Wonder how many clients have underrated change over switches as a result of incorrect advice received, but more importantly,
    it seems as if there are "sparkies" out there who also don't understand this because the same lad said " these 35A units are flying off the shelves".

    I bought the 63A unit and left, shaking my head in disbelief.

    In my opinion, MCE should not even make a 35A change over switch mounted in an enclosure and labelled eskom .. off .. generator.
    Cannot think of an installation where it would work and not be underrated.

    Am I missing something ?

    Peace out .. Derek

  2. #2
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,479
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Maybe the 35A is "switching rating" not carrying current rating, but rather break and make current rating.
    Once a switch has closed, the current flow through it can be much higher, provided you do not open the switch.

    In the case that it is used here, the chances that the switch will disconnect a heavy load is highly unlikely, and hence the reason they are getting away with.

    Even so, there is a reason why one must read and understand "Specifications"
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  3. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    Quote Originally Posted by Derlyn View Post
    In my opinion, MCE should not even make a 35A change over switch mounted in an enclosure and labelled eskom .. off .. generator.
    Cannot think of an installation where it would work and not be underrated.

    Am I missing something ?

    Peace out .. Derek
    Hi

    We would use the 35Amp switch , create an essential DB with protection of 25Amps whether we feed mains or generator to stay within the SANS 10142 code 7.12.2.4
    In PE I don't believe you can use the 63Amp switch as the Municipal mains CB in the meter box is generally 80 amp and would not offer the protection as most domestic installations have isolators as a main switch.

    We also use smaller change over switches on geyser element/heatpump installations and UPS installations -

    To me there is a need for smaller changeover switches

    To answer your question " Am I missing something " - yes you are

    7.12.2.4 Where the alternative supply is intended to provide a supply to an
    installation that is not connected to the main supply, or to provide a supply
    as a switched alternative to the main supply, the capacity and operating
    characteristics of the alternative supply shall be such that danger or damage
    to equipment does not arise after the connection or disconnection of any
    intended load as a result of the deviation of the voltage or frequency from the
    standard range. Means shall be provided to automatically disconnect such
    parts of the installation, as may be necessary if the capacity of the
    alternative supply is exceeded

  4. #4
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,479
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Provided of course that the full load from the municipality is not being switched through the change over switch, if the main supply is rated above the 35A.
    In my case I have a 3 phase 80Amp mains supply, where the whole load is switched through the change over switch when the generator runs.

    The original 80A change over from ACDC, Neutral contact burnt out when it was running off the municipal supply, and we replaced it with the 100A.

    So it depends, if you are only using it to switch a partial load at the site, then the 35A may be more than adequate.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  5. #5
    Diamond Member
    Join Date
    Apr 2010
    Location
    planet earth
    Posts
    3,943
    Thanks
    153
    Thanked 317 Times in 287 Posts
    Quote Originally Posted by GCE View Post

    7.12.2.4 Where the alternative supply is intended to provide a supply to an
    installation that is not connected to the main supply, or to provide a supply
    as a switched alternative to the main supply, the capacity and operating
    characteristics of the alternative supply shall be such that danger or damage
    to equipment does not arise after the connection or disconnection of any
    intended load as a result of the deviation of the voltage or frequency from the
    standard range. Means shall be provided to automatically disconnect such
    parts of the installation, as may be necessary if the capacity of the
    alternative supply is exceeded
    Any tips on devices that can be used to automatically disconnect heavy loads?

    I have looked into no volt relays and solid state relays being switched using the higher frequncey remote devices.

    Also wifi ... to unstable and boosters required at a cost.

    Bluetooth ... distances too far ... also boosters required.
    Comments are based on opinion...not always facts....that's why people use an alias.

  6. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    A few of the inverters are coming out with voltage free contacts to be able to disconnect load on grid out .
    No volt relays still the most reliable
    There are smart relays that will drop load when you draw more then say 20 Amps.

    To me they all run the risk of failure and I rather ensure that the load on the inverter side is well within the ratings and loading that are needed which saves inverter life and battery life

  7. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,484
    Thanks
    104
    Thanked 141 Times in 134 Posts
    Quote Originally Posted by Justloadit View Post
    Provided of course that the full load from the municipality is not being switched through the change over switch, if the main supply is rated above the 35A.
    In my case I have a 3 phase 80Amp mains supply, where the whole load is switched through the change over switch when the generator runs.

    The original 80A change over from ACDC, Neutral contact burnt out when it was running off the municipal supply, and we replaced it with the 100A.

    So it depends, if you are only using it to switch a partial load at the site, then the 35A may be more than adequate.
    Here in Emonti soon to be Egompo the mains is connected to the switch , the genny to the switch and 95% of the time, the houses DB is the load.

    That's why I said I shudder to think how many under rated switches have been installed.

    Peace out .. Derek

Similar Threads

  1. P2 change over switch diagram pg344 Sans10142-1:2020 edition 3
    By melvinbrucepaton in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 18-Sep-20, 02:08 PM
  2. Change over switch for a Inverter
    By Daveleigh in forum Electrical Load Shedding Forum
    Replies: 1
    Last Post: 05-May-20, 05:11 PM
  3. [Question] Help with hob plate/switch
    By Houses4Rent in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 08-Apr-17, 07:43 AM
  4. Pastel V11 - Change in year end and change in # of periods
    By OlgaSaavedra in forum Accounting Forum
    Replies: 5
    Last Post: 09-Jul-15, 07:07 PM
  5. Main Switch?
    By Sparks in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 08-Feb-11, 10:16 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •