Thread: Wiring of pump controller

  1. #11
    New Member
    Join Date
    Feb 2019
    Location
    Nairobi
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Connecting Automatic Water Pump

    Quote Originally Posted by Justloadit View Post
    It seems that the controller assumes you have a capacitor start and run motor with a built in mechanism to take care of the start capacitor, which you generally will not find with a submersible pump.
    The U and V connections from the controller would simply go to the 2 wires of your motor supply cable.
    Hi,
    I have recently acquired an Automatic Water Pump Controller and I need to connect it to the water pump. On the circuit board, there is L, N and E which definitely connects to the mains.
    On the lower side I have E, U and V. My question is, can I power the water pump from these terminals labelled E, U and V?
    If this is the case, then between U and V which one is live or Neutral.
    Remember on the water pump there is already a power cable that I currently use to connect to the mains.

    Moses Madegwa
    Last edited by Dave A; 03-Feb-19 at 05:10 AM.

  2. #12
    New Member
    Join Date
    Feb 2019
    Location
    Nairobi
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Madegwa View Post
    Hi,
    I have recently acquired an Automatic Water Pump Controller and I need to connect it to the water pump. On the circuit board, there is L, N and E which definitely connects to the mains.
    On the lower side I have E, U and V. My question is, can I power the water pump from these terminals labelled E, U and V?
    If this is the case, then between U and V which one is live or Neutral.
    Remember on the water pump there is already a power cable that I currently use to connect to the mains.

    Moses Madegwa
    Thanks Justloadit
    Just to clarify, currently I have the water pump, and it connects directly to the mains through a fused 3-pin 13 amp plug. Now I need to connect the water pump through the automatic pump controller which I have just acquired.
    So should I remove the 13 amp plug, then I connect the wires from the water pump (L, N and E) to the U, V and E on the pump controller directly?

  3. #13
    Diamond Member Justloadit's Avatar
    Join Date
    Nov 2010
    Location
    Johannesburg
    Posts
    3,479
    Thanks
    134
    Thanked 695 Times in 593 Posts
    Blog Entries
    1
    Quote Originally Posted by Madegwa View Post
    Thanks Justloadit
    Just to clarify, currently I have the water pump, and it connects directly to the mains through a fused 3-pin 13 amp plug. Now I need to connect the water pump through the automatic pump controller which I have just acquired.
    So should I remove the 13 amp plug, then I connect the wires from the water pump (L, N and E) to the U, V and E on the pump controller directly?
    In that case the answer is - Yes. But ensure that the switch contacts are rated for your motor current.
    Victor - Knowledge is a blessing or a curse, your current circumstances make you decide!
    Solar pumping, Solar Geyser & Solar Security lighting solutions - www.microsolve.co.za

  4. #14
    New Member
    Join Date
    Apr 2019
    Location
    Pretoria
    Posts
    1
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Justloadit View Post
    In that case the answer is - Yes. But ensure that the switch contacts are rated for your motor current.
    Hi, which of the 2 ( U &V) is live or neutral?

  5. #15
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,236
    Thanks
    34
    Thanked 304 Times in 258 Posts
    On a single phase motor rated at 220v it would be immaterial and make no difference
    Generally U would be live

Page 2 of 2 FirstFirst 12

Similar Threads

  1. [Question] Wiring under thatch
    By camrad in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 07-Sep-17, 05:32 AM
  2. open wiring
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 48
    Last Post: 29-Nov-14, 09:25 AM
  3. Pump with Pressure Tank ???
    By tec0 in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 03-Nov-13, 10:52 AM
  4. [Opinion] What type of wiring?
    By 123 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 22-Apr-10, 11:32 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •