    bathrooms and fixed appliances

    what are the regulations with regards to a mirror with lights in a bathroom in lets say zone 2...100 mm away fron the shower without a door.

    if you have an extractor fan directly above your shower which regulations would you take note of...if the extractor is connected to the light fitting and is above 2.5 metres from ther shower basin...what is the zone just above the shower and what if it is extracting the steam?

  2. #2
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    even better still...what about a fixed appliance mounted at 2.6 m above the shower basin if the shower rose is 2.1 metres above the shower basin? which regulation to use?

  3. #3
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    if you have an extractor fan directly above your shower which regulations would you take note of...if the extractor is connected to the light fitting and is above 2.5 metres from ther shower basin...what is the zone just above the shower and what if it is extracting the steam?
    i wouldnt worry about the fan as the motor is in the ceiling area and the housing is plastic.if its extracting steam ,its not going to extend the zone,as its not as if the steam is flammable. if its connected to the light then the light switch should be double pole.
    Last edited by Dave A; 17-Jun-11 at 05:25 AM. Reason: format help

  4. #4
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    Quote Originally Posted by bergie View Post
    i wouldnt worry about the fan as the motor is in the ceiling area and the housing is plastic.if its extracting steam ,its not going to extend the zone,as its not as if the steam is flammable. if its connected to the light then the light switch should be double pole.
    or on earth leakage

  5. #5
    Junior Member
    Join Date
    Jun 2011
    Location
    JHB
    Posts
    19
    Thanks
    4
    Thanked 0 Times in 0 Posts
    All bathroom appliances including mirror lights should be on earth leakage.
    It's allso regulation to have ceiling fans on earth leakage.

  6. #6
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    Quote Originally Posted by TECHNICIAN 810 View Post
    All bathroom appliances including mirror lights should be on earth leakage.
    It's allso regulation to have ceiling fans on earth leakage.
    in which zone?

  7. #7
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Table 7.1 ― Conditions under which electrical equipment
    may be installed in a bathroom
    1 2 3 4
    Conditions that apply in
    Electrical equipment Zone 1 Zone 2 Zone 3
    Distribution and control X X Normal provisions of this
    part of SANS 10142
    Bell push B1 and C1 B1 and C1 Normal provisions of this
    part of SANS 10142
    Socket-outlet X C2 Normal provisions of this
    part of SANS 10142
    Wall switch X X Normal provisions of this
    part of SANS 10142
    Pull switch Normal provisions of this part of SANS 10142
    Distribution boards X X X
    Fixed appliances
    (including luminaires)
    (A and B1)
    or
    (B2)
    (A and B1)
    or
    (B2)
    Normal provisions of this
    part of SANS 10142
    The symbols used in this table are the following:
    A denotes that earth leakage protection shall be provided;
    B1 denotes that the equipment shall be so enclosed in insulating material that it is not
    possible to touch current-carrying parts with the standard test finger;
    B2 denotes that class II appliances shall be used;
    C1 denotes that the equipment shall be supplied from a safety supply with a secondary
    voltage not exceeding 25 V;
    C2 denotes that the equipment shall be supplied from a safety supply that has a
    maximum rating of 50 VA. Shaver supply units shall comply with SANS 61558-2-5/
    IEC 61558-2-5 (SABS IEC 61558-2-5).
    X denotes that the equipment shall not be installed.
    Amdt 1

    7.1.4.3.1 In zones 0, 1 and 2, no switchgear and accessories shall be
    installed except that emergency push buttons, which operate at a safety
    extra low voltage at nominal voltage not exceeding 12 V, are permitted in
    zones 1 and 2.

    Zone 1 is limited by
    a) the vertical plane circumscribing the outer edge or 0,20 m from the
    inner edge (where the ledge is too wide) of the bathtub, shower basin,
    or for a shower without a basin, by the vertical plane 0,60 m from the
    shower rose,

  8. #8
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    In other words, neither the fan nor the lights are acceptable.
    Maybe Dave can get the table to display correctly.
    Pasting is a whole lot faster than I can type.

  9. #9
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    zone 1-2 only extend to 2.5 m which means at 2.6 m it is out of the zone 1 and 2...zone 3 rules apply.

  10. #10
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    Almost but not quite, it extends to "at least 2500mm" and then must be read with "600mm above the shower rose".