    Contactor Question

    Today i replaced the switchgear on a star delta circuit. Simple enough ....
    When i pressed start nothing happens. So i realized my coil voltage was not right. So i took the old coils and put them in the new contactors.
    The first question is would it damage a contactor or its coil if i gave it 110V on a 22Ov coil? I'm thinking no???
    So then the circuit works after the change exept when delta pulls in the contactor chatters and shakes heavy before it pops the fuse on the transformer. So what could cause this?
    Nothing wrong with the wiring because when i put the old contactor back it worked fine.
    So it could be the coil but it was working an hour before i started, only thing i can think of is that it might be a dud contactor? is that possible?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Dud contactor is a long shot but it's possible. The phrase '.......but it was working an hour before i started' would be the hint of a more likely cause, check the circuit you've worked on and every termination.

    110v across a 220v coil won't cause a problem for the coil, it's more likely to cause burning or arcing at the actual load contacts due to slow and sluggish operation.

    In general a contactor that has sufficient voltage to bring it in will stay in without chattering. The voltage required for it to operate from scratch is higher than the voltage required to hold it in once it's operated. Chattering is more likely to happen if there's a poor connection, or incorrect wiring where the coil supply is being interrupted due the the operation of the contacts. Possibly specifying a contactor with a normally closed aux contact instead of a normally open one or vice versa but this would be obvious with the contact numbering.

    The only other thought I had was that you should check to see that the coils is AC rated not DC but this is a more common issue with 24volt coils than 220 volt ones.
    _______________________________________________

    _______________________________________________

  3. #3
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    The other reason for chattering could be a voltage drop when the load comes in...

  4. #4
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    the delta contact on the timer could be damaged, or the n/c on the star contactor . connect 110 volt direct on to the coil and see if it works. hope you have mechanical interlocks.it could be expensive if both come in at the same time.

  5. #5
    Gold Member Martinco's Avatar
    Join Date
    Oct 2008
    Location
    Rustenburg
    Posts
    927
    Thanks
    175
    Thanked 136 Times in 108 Posts
    I have experienced this before and what happened when I stripped the top of the contactor to replace the coil, I inadvertently rotated the top part by 180 degrees which caused the mating surfaces on the core to be 180 degrees out. I can only assume that the copper strips embedded into the laminated core had something to do with the chattering of the contactor.
    Martin Coetzee
    Supplier of Stainless Steel Band and Buckle and various fastening systems. Steel, Plastic, Galvanized, PET and Poly woven.
    We solve your fastening problems.
    www.straptite.com

    You may never know what results will come from your actions, but if you do nothing, there will be no results... Rudy Malan 05/03/2011

  6. #6
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    Quote Originally Posted by Gei View Post
    Today i replaced the switchgear on a star delta circuit. Simple enough ....
    When i pressed start nothing happens. So i realized my coil voltage was not right. So i took the old coils and put them in the new contactors.
    The first question is would it damage a contactor or its coil if i gave it 110V on a 22Ov coil? I'm thinking no???
    So then the circuit works after the change exept when delta pulls in the contactor chatters and shakes heavy before it pops the fuse on the transformer. So what could cause this?
    Nothing wrong with the wiring because when i put the old contactor back it worked fine.
    So it could be the coil but it was working an hour before i started, only thing i can think of is that it might be a dud contactor? is that possible?
    are you sure the n/o and n/c contacts on the control circuit are the same

  7. #7
    Junior Member
    Join Date
    Jul 2009
    Location
    Port Elizabeth
    Posts
    17
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks for all the replies, Found where i made the mistake, When i stripped the contactor to change the coil the iron core that holds the coil in place fell out and i did not notice this. Found it the next day on the floor. This will teach me to strip the thing while its still mounted in the panel with wires attached. To much of a rush and to lazy to take it out. Cheers

  8. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Thanks for the follow-up, it's always interesting to find out what the problem was in the end.
    _______________________________________________

    _______________________________________________

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •