    cable sizes

    anybody know where to get tables for working out cable ratings.
    i have to quote on a 850 amp supply. it is in a trench most of the way and 52m long.
    i normally have to phone aberdare in joburg. the technical guy worked it out to 3x 240mm 4 core armoured cables.seems a bit of an overkill.would work out to over R 160 000 just for cable.

  2. #2
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    if it is underground in a trench i also get 3 x 240mm

    i am sure you know this already...but just watch the fault levels when selecting equipment and cables for that matter...

    i did a project last year and was advised by everyone to use parallel cables but due to the fault level calculated at the 200 kw motor we had to use 1 x 185.

  3. Thanks given for this post:

    bergie (17-Mar-11)

  4. #3
    Bronze Member mikilianis's Avatar
    Join Date
    Dec 2008
    Location
    Cape Town South Africa
    Posts
    125
    Thanks
    164
    Thanked 8 Times in 7 Posts
    The fault levels do you mean p.s.c. or am I on the wrong path