    Touch Voltage

    Guys I am finding it difficult to answer this question:

    "Calculate from the basic principles the maximum value of the protection device if the following is given:

    Length ECC is 69m with an area of 6mm2"

  2. #2
    Junior Member
    Join Date
    Nov 2010
    Location
    Durban
    Posts
    21
    Thanks
    0
    Thanked 1 Time in 1 Post
    Calculate from basic principles the maximum value of the protection device, if the following is given:
    the length of ECC (earth continuity conductor) is 69 meters of copper with an area of 6mm2.

    For questions like this, remember two things: The first is that the maximum allowed touch voltage (T.V.)
    according to the code is 30V. Use this formula:

    Touch Voltage = 2 x I(CB) x R(ECC)

    Where,
    I(CB) is the value of the protective device (Circuit Breaker or Fuse) = the value to be calculated
    R(ECC) is the resistance value of the Earth Continuity Conductor = we are given the size of the conductor
    Touch Voltage (T.V) = 30V

    The second thing: if you can recall from the previous post (voltage drop calculations) that the resistance in Ohms can also be
    expressed in the following form:

    R = (Value of R in Ω/Km x L in meters)/1000m [Ohms]

    Please remember to use Table E1 for the value of R in Ω/Km for each given conductor size.

    For this question:

    ICB =? [That is what we are asked to calculate]

    We can calculate: The value of R given in Ω/Km for 6mm2= 3.6 Ω/Km [From Table E1]
    The length is L = 69m

    Substituting values we have, R = (Value of R in Ω/Km x L in meters)/1000m [Ohms]

    = (3.6 Ω/Km x 69m)/1000m = 0.2484 Ω

    Substituting values in our touch voltage formula
    we have, T. V. = 2 x I(CB) x R(ECC)

    30V = 2 x I(CB) x 0.2484 Ω

    I(CB) = 30V/0.4968Ω = 60.3865A

    Therefore the value of the protective device is 60A

    For this question and many more you may visit:
    http://www.installationrulesstudymate.co.za

    We have developed study tools for the Installation Rules Exams.
    The study tools provided on our website are jam-packed with questions
    and worked out examples based on the actual Installation Rules Exams
    written over the last few years. The questions you will find in the study
    tools are questions similar in nature to the type you will find on the actual
    Installation Rules Exams. Both the Study Guides and the Exam Simulator
    Software contains sufficient questions which are presented in the same
    format used on the actual exam.

  3. #3
    Junior Member
    Join Date
    Sep 2010
    Location
    Windhoek
    Posts
    14
    Thanks
    4
    Thanked 0 Times in 0 Posts
    Thanks. I though the TV is 25V. I will check your site out

Similar Threads

  1. Extra low voltage lighting question
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 13-Mar-11, 08:37 AM
  2. Mains voltage logger
    By duncan drennan in forum Technology Forum
    Replies: 16
    Last Post: 05-Feb-11, 03:33 PM
  3. Touch safe office equipment testing
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 28-Sep-10, 11:39 PM
  4. Difference between: Power factor correction, Voltage regulation and Voltage stabisizi
    By BigRed in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 08-Feb-10, 09:29 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •