Results 1 to 10 of 11

Thread: November 2010 Paper 2 Exam Question 1 and Question 2 (ANSWERS)

Threaded View

Previous Post Previous Post   Next Post Next Post
  1. #1
    Junior Member
    Join Date
    Nov 2010
    Location
    Durban
    Posts
    21
    Thanks
    0
    Thanked 1 Time in 1 Post

    Installation Rules Paper 2 (November 2010 Exam Question 1 and Question 2 -ANSWERS)

    PAPER 2 QUESTION 1 OF NOVEMBER 2010
    THREE PHASE AC CIRCUITS: PROSPECTIVE SHORT CIRCUIT CURRENT


    1. Calculate the PSCC for a three phase fault if the following information is given:

    *Transformer capacity 200 kVA at 400/250 volt
    *Transformer protection 200 amp per phase
    *70 mm2 4 core copper cable + ECC of 100 meters
    *Z% of the transformer is 5% ohm

    2. Calculate the touch voltage at the load if the ECC is the same size as one of
    the phase conductors

    3. What is the total loop impedance for the circuit?

    ANSWERS

    1. 2.26 kA

    2. 12.748 V

    3. 0.1037418 Ohm

    Hint For Question 3:
    Z(Total) = Z(Transformer) + Z(Phase Conductor) + Z(PEN or PE Conductor)


    PAPER 2 QUESTION 2 OF NOVEMBER 2010 VOLTAGE DROP CALCULATION

    A 1 kW single phase electrical motor is used as part of a lift system to hoist and deliver a 4 tons of bricks per hour at a building site.
    If the supply voltage is 230 V at the basement of the lift with the dumping floor level 65 m higher, calculate the following:

    2.1 The percentage volt drop just before the load is dumped (7 Marks)**

    NOTE: Take a motor power factor of 0,9 with a hoist speed of 100 r/min through the reduction gearbox when fully loaded. Use a 3 core PVC armoured copper cable of 4 mm2 for the entire installation

    2.2 The resistance of the ECC (1 Mark)**

    2.3 The touch voltage at the motor if a 5 amp circuit breaker is used (2 Marks)**

    ANSWERS
    2.1 1.50%

    2.2 0.3575 Ohm

    2.3 3.575V


    I have not provided you with the full solution for this section but I have provided answers, try them out and if you have any problems email me and I will provide you with the full solution (Provided that you email me your attempt).

    You may visit the installation Rules Study Mate Website http://www.installationrulesstudymate.co.za or send email to info@installationrulesstudymate.co.za

    To find out how you can get the full solution to the above questions and many more.

    Your Personal Tutor: Installation Rules Paper 1 and Paper 2
    Leonard Fikani Ndlovu
    Cell: 072 634 8547
    Last edited by Fikani2010; 02-Feb-11 at 02:12 AM.

Similar Threads

  1. [Article] Installation Rules Paper 2 (April 2010 Exam Question 1) Answer
    By Fikani2010 in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 21-Nov-17, 09:38 AM
  2. Question.
    By nilla in forum General Business Forum
    Replies: 3
    Last Post: 26-May-10, 07:08 PM
  3. [Question] NCA question
    By Khomani in forum National Credit Act Forum
    Replies: 0
    Last Post: 28-Sep-09, 11:13 AM
  4. A strange question about VAT.
    By insulin in forum Tax Forum
    Replies: 7
    Last Post: 09-Mar-09, 08:45 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •