    Wiring under thatch

    What is the correct method of wiring lights under a thatch, Must all wiring be in Conduit or is norse cable meeting the standards. Sans 10142 only refer to open wiring . Is norse catalogued as open wiring.
    Last edited by camrad; 16-Oct-10 at 08:14 AM.

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Can you provide a link to the specifications of 'Norse' cable?
    _______________________________________________

    _______________________________________________

  3. #3
    New Member
    Join Date
    Oct 2010
    Location
    Johannesburg
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    1.5 mm 2 + E round norsk

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    If it's similar to surfix cable then the cable would only be classed as open wiring when stripped of its outer sheath.

    [quote sans0142]6.4.5 Open wiring
    NOTE Open wiring consists of single-core insulated conductors that operate at not
    more than 250 V to earth.
    [/quote]

    If the cable is installed at least 1 meter below the thatch then it can be run as cable only. If it's closer than 1 meter to the thatch material then the cable must be shielded and earth bonded.
    5.2.2.4 Clearance distance between the thatch and the metal objects under the thatch
    Metals used in the construction of a thatched roof shall be bonded and earthed. Water pipes, vent
    pipes, tanks, gas pipes, antennas, telephone and bell wires, burglar alarms and electrical wiring and
    conduit within 1 000 mm of the thatch shall be shielded, bonded and earthed
    (see SANS 10142-1).
    Last edited by Dave A; 17-Oct-10 at 06:53 AM.
    _______________________________________________

    _______________________________________________

  5. Thanks given for this post:

    mikilianis (17-Oct-10)

  6. #5
    Email problem 123's Avatar
    Join Date
    Mar 2010
    Location
    South Africa
    Posts
    57
    Thanks
    25
    Thanked 5 Times in 5 Posts

    Reg 5.2.2.4

    Hi Andy, pse direct me to the page where the above regulation is? (Sans 10142:2009 Edition 1.7) Thanks.
    If it is not broken, fix/test it until it is.
    This is my opinion and I stick to it.

  7. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by 123 View Post
    Hi Andy, pse direct me to the page where the above regulation is? (Sans 10142:2009 Edition 1.7) Thanks.
    Sorry for the confusion. SANS0142 only refers to bare wiring being 1000mm below thatch for extra low voltage lighting installations.
    SANS 10313 (The protection of structures against lightning) refers to 'metal objects under thatch and their earth bonding requirements. This encompasses electrical wiring, alarm wiring, telephone wiring etc.
    SANS 10313:2005 Edition 2.1
    5.2.2.4 Clearance distance between the thatch and the metal objects under the thatch

    Metals used in the construction of a thatched roof shall be bonded and earthed.
    Water pipes, vent pipes, tanks, gas pipes, antennas, telephone and bell wires, burglar alarms and electrical wiring and conduit within 1 000 mm of the thatch shall be shielded, bonded and earthed (see SANS 10142-1).
    _______________________________________________

    _______________________________________________

  8. #7
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    In the SANS 10313 quote it says 'see SANS 0142-1' but I don't see where it ties in with this reg.
    _______________________________________________

    _______________________________________________

  9. #8
    New Member
    Join Date
    Aug 2017
    Location
    Randfontein
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts
    I hope someone can supply a quick answer. I have just been at an installation where the installation electrician installed flat 2 + E inside the thatch in the grass so the wire is not visible. there are no joints but the client is not entirely happy with this there is also other wiring which is norch. Can anyone help me with the confirmation that this is in order on the SANS code as I cannot seem to find that this is OK or confirmed in order. The wire is not open like old type installation.

  10. #9
    Full Member
    Join Date
    Jun 2016
    Location
    Port Elizabeth
    Posts
    28
    Thanks
    0
    Thanked 1 Time in 1 Post
    Hi
    Found this in the regs and hope it helps.
    6.4.8 Wiring through building elements 6.4.8.1 If wiring has to pass right through a building element such as a floor, a wall, a partition, or a ceiling, conductors and busbars shall be in a non-flammable enclosure or wireway. 6.4.8.2 If the building element is a fire break, the space around a) a cable, b) a wireway, or c) the wiring in a wireway, if the internal cross-sectional area of the wireway exceeds 13 000 mm2, shall be completely filled with non-flammable material over the full thickness of the building element. NOTE 1 Mineral wool is non-flammable.

  11. #10
    New Member
    Join Date
    Aug 2017
    Location
    Randfontein
    Posts
    2
    Thanks
    0
    Thanked 0 Times in 0 Posts

    Wiring in t,hatch

    Thanks for the info. There seems to only be notes on specs of wiring distance from thatch and relates to open wiring being GP, my choice would have been surface along the wooden parts in conduit no matter what type of wire just for safety sake. The client has spoken to SABS and they confirm no wire in thatch. His insurance broker says WTH, if it burns it burns they can't prove what happenened so they iust carry on, but that attitude will probably change when it does happen

Similar Threads

  1. [Opinion] What type of wiring?
    By 123 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 22-Apr-10, 11:32 PM
  2. electrical standards
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 9
    Last Post: 06-Jan-08, 03:31 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •