    kA ratings

    Right, just making sure of myself before i tell someone on site to naff off. I did an estimate for a shop fit with an existing DB and in the estimate at the bottom I put that "its is assumed that the existing installation and any part to be reused is compliant SANS 0142". Now I looked at the board, it looked ok, the sparks on site ran a new sub main to it, not my problem down to them to COC that. Now when I do the COC for these shops I always state that the COC only covers work that I have done and does not cover anything prior to the DB, reason being you can shut down large sections of shopping centers to inspect submains, they won't allow this and sign the COC where they should accepting this. Now I did my dead tests, earth continuity, Insulation resistance etc. All perfect. Now I do the Earth Fault loop Impedance and PSC at the board and find the prospective earth fault current is 7.7kA, Higher than I thought it would be but I trust my Fluke 1653B. The breakers protecting the existing circuits which i haven't touch altered or changed in anyway have 2.5kA breakers on them. The main switch is a 63 amp circuit breaker rated at 6kA and the earth leakage covering the Sockets is 63 amp 30mA with breaking capacity of 2.5kA.
    Now I am going to fit a breakers with breaking capacity of 10kA to cover the circuits I have installed(4 lighting circuits and 1 socket circuit).
    The problem is that the guy on site says can't be 7.6kA and won't change the main switch to a higher kA rating and I say well I won't sign the COC. Its not unfeasible for a fault to occur at the DB(cable trapped in door or cover isn't unheard of) which could have a very high fault current, certainly enough to destroy a breaker rated at 2.5kA. I am not signing of any of the existing circuits connected to the board. I figure they changed the sub main thus changing the characteristics of the board and those circuits.

    So am I right in saying that I am not responsible for the existing circuits if I state as such in the COC and put in section 3 only the circuits which i have installed and I am right to insist on them changing the main switch to be able to cope with the possible fault current that could occur to enable me to sign of the work I have done. Your opinion appreciated.

    By the way the DB (fed in 3 core 16mm SWA) is just a few meters away from the main incomer, reason for high PSC

  2. Thanks given for this post:

    mikep (07-Jan-15)

Similar Threads

  1. Eskom or the wind ?
    By daveob in forum General Chat Forum
    Replies: 11
    Last Post: 05-Oct-10, 06:59 AM
  2. Listener AR ratings - how they work?
    By garthu in forum Marketing Forum
    Replies: 1
    Last Post: 29-Aug-10, 10:23 PM
  3. Downrated credit ratings - how will this affect us?
    By Dave A in forum Business Finance Forum
    Replies: 1
    Last Post: 13-Nov-08, 08:13 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •