    junction box

    i was called today to attend to a light circuit tripping when it rains...
    they suspect that it could be the new light which was installed recently.

    the cable on the left is an armoured cable.

    there are other lights further down the fence...my concern is that the lights are all pvc light fittings with pvc lampholders...but the armoured cable earth wires are cut off at the first light which means that there is no earth further down...

    what do you think should there be some sort of earth continuity thru out the length of the cable even though the fittings are pvc?

    what do you think about the pvc pushin gland holding the armoured cable in the box?

    what do you think about the standard junction box out in the weather (daves inspectors know the answer to this one from the job in westville) do you think i am being unreasonable requesting a weather proof box?

    no rain drip on the cables?

    not even silicon around the lid?

    loose glands holding the cable?

    cabtryre from the box to the lamp holder?

    glands are not glued into te box as you can see it is pulling out on the left hand side because the cable is short.

    i think i should request the coc for the light installation...or do you think its not neccessary to issue a coc for one light?

    a list this long for such a small item?

    i would hate to see any other work done by this person...i would jam up daves band width.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	Juntion box .jpg 
Views:	273 
Size:	67.7 KB 
ID:	1382  

  2. #2
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Quote Originally Posted by murdock View Post
    i was called today to attend to a light circuit tripping when it rains...
    So did you find the fault?

  3. #3
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    not yet because i dont feel this is the only issue...i believe the next thread i wrote about the db is half the problem...connecting an electric fence to an e/l unit...

    other light fittings which are filling up with water...

    what i am puzzled about is that there is no earth continuity on the light circuit as i mentioned so why is the e/l unit tripping and not the circuit breaker tripping because of a dead short from the water between live ad neutral?

  4. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by murdock View Post
    .my concern is that the lights are all pvc light fittings with pvc lampholders...but the armoured cable earth wires are cut off at the first light which means that there is no earth further down...

    what do you think should there be some sort of earth continuity thru out the length of the cable even though the fittings are pvc?
    The SWA cable must terminate at both ends on an SWA gland andshould be earth bonded at source. If the fittings are of such a class that earthing is unnecessary then the gland on both the incoming and outgoing cable should have an earth ring and a lugged earth wire connecting them to give earth continuity. If all the fittings are PVC then you could probably omit the separate earth wire that should run with the SWA cables.

    Quote Originally Posted by murdock View Post
    what do you think about the standard junction box out in the weather (daves inspectors know the answer to this one from the job in westville) do you think i am being unreasonable requesting a weather proof box?
    Apart from inadequate IP rating conduit boxes aren't UV stabilised and can't be mounted in view of the sun.
    Quote Originally Posted by murdock View Post
    no rain drip on the cables?

    not even silicon around the lid?

    loose glands holding the cable?

    cabtryre from the box to the lamp holder?

    glands are not glued into te box as you can see it is pulling out on the left hand side because the cable is short.
    This was probably installed DIY or by a handyman (I hope). Any certification will be out of the question. I would just reinstall it using as much of the existing materials as possible then give a COC just for the work done; it probably won't take any longer than trying to localise an intermittent tripping fault on the circuit as it is.
    _______________________________________________

    _______________________________________________

Similar Threads

  1. sans junction box
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 20-Mar-10, 10:13 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •