    Question why do lights blow regularly on one circuit & very seldom on another, both supplied f

    This is for those with much past experience!!
    Could someone shed light on why lights on one light circuit fuse regularly and on other circuits almost never?
    Consider this scenario:
    A circuit on a 10A breaker, using FT&E 1.5mm^2 feeds a three lever 1w switch, 1st switches ceiling fan with 3 lamps, 2nd an outside floodlight and the 3rd 6 x lamps connected in parallel (60W bulbs) outside but under cover. It's the last mentioned circuit that is under question. These lights are constantly being replaced yet the others, as well as lights in the rest of the installation, hardly ever need to be replaced. All is correct as far as the wiring goes, the supply voltage acceptable at the time of measuring, although I can't say what the situation is like all the time. Can someone suggest a possible cause - other that poor quality lamps. CFL's have been tried as well and they don't last either.

  2. Thanks given for this post:

    mikilianis (20-Sep-10)

  3. #2
    Email problem
    Join Date
    Sep 2010
    Location
    cape town
    Posts
    308
    Thanks
    3
    Thanked 43 Times in 37 Posts
    if the fittings are old or have very low quality lamp holders then proper contact isnt made with the lamp. the contacts heat up and blows the lamp. try replacing some or all of the fittings.

  4. Thanks given for this post:

    mikilianis (20-Sep-10)

  5. #3
    Diamond Member
    Join Date
    Mar 2010
    Location
    Cape Town
    Posts
    6,329
    Thanks
    426
    Thanked 978 Times in 795 Posts
    I've have had lights blow on the same circuit over at the moment the light is turned on.

    I would hazard a guess that the switch is faulty. Could be that the contacts bounce.

  6. Thanks given for this post:

    mikilianis (20-Sep-10)

  7. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    I've had similar problems a couple of times in the past. One was fixed by just remaking all terminations and connections on the circuit. The second one was caused by a poor connection on the incoming supply neutral in the main DB. Because it was a 3-phase DB the neutral bar was at a floating voltage which caused over-voltage damage to the lighting and a couple of appliances.
    _______________________________________________

    _______________________________________________

  8. Thanks given for this post:

    mikilianis (20-Sep-10)

  9. #5
    New Member
    Join Date
    Sep 2010
    Location
    Eastern Cape
    Posts
    8
    Thanks
    1
    Thanked 2 Times in 2 Posts

    why do lights blow regularly on one circuit & very seldom on another

    Thanks bergie, adrianh & AndyD.
    It's fascinating posting a problem and getting such varied responses, which is the value of this forum. All possible causes suggested could apply and since the board in question is supplied from a 3ph source the post from Andy cannot be ruled out. An interesting point is that one of the six lights has just recently been added, is a brand new fitting with an ES fitting which should make good contact, a new bulb installed only lasted a couple of days! I will take all suggestions into consideration and apply as a process of elimination & see what turns out.
    Thanks again.

  10. Thanks given for this post:

    mikilianis (20-Sep-10)

  11. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    You're welcome harveya. I forgot to ask, does the unreliable circuit have a dimmer on it as well as a lever switch? Most CFL lamps won't run with a dimmer, there are a couple of models which you can use a specific leading or trailing edge PWM dimmer but these are few and far between.

    Good luck sorting it out.
    _______________________________________________

    _______________________________________________

  12. #7
    New Member
    Join Date
    Sep 2010
    Location
    Eastern Cape
    Posts
    8
    Thanks
    1
    Thanked 2 Times in 2 Posts
    Morning Andy. No dimmer on this circuit, just a straightforward light circuit with 6 lamps on it!

  13. #8
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    i would do a loop impedance test on the circuit...megger the circuit and fit a recorder.

    sometimes when there is a low insulation reading it will pop the lamps.

    i assume they are on the same phase because they go thru a 3 lever switch?
    are there big compressors or heavy loads close by?
    is the building earthed correctly?
    are the lamps rated for the correct voltage?
    are the lights all on all day or do some switch on at night and others during the day...ie are they all on at the same time?
    you said es lamps are they all connected to the correct polarity.
    has this issue started recently since the new fitting was installted or has it been problem for a long time?

    we can only guess without prior knowledge of the insallation

  14. #9
    Email problem Master Electrician's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    28
    Thanks
    3
    Thanked 33 Times in 12 Posts
    I would like to suggest that there is a faulty capacitor or discharge resistor in the ceiling fan in circuit 1. It is discharging through the lighting circuit instead of the discharge resistor.

  15. #10
    Bronze Member mikilianis's Avatar
    Join Date
    Dec 2008
    Location
    Cape Town South Africa
    Posts
    125
    Thanks
    164
    Thanked 8 Times in 7 Posts

    Question

    How would the capacitor discharge through the lighting circuit ?