    Advice

    Hey all,
    I need to issue a COC but refuse because the factory is not up to scratch.I have been at it for 3 months now and still not finished.(I am permanently employed by them)The fact that my job is on the line does not bother me.I try to be honest all the time and this factory will not pass in any way. The bosses son has brought in a "tame" sparky who will issue a COC for the factory as it stands.Can I post some pics and details and you guys tear it apart and tell me who is wrong?

    Some examples as a teaser:
    1)50 mm 4 core rubber trailing cable 70mts long used as a permanent supply to a test bench with a step up transformer with no safety equipment and only a 400 amp breaker to switch the transformer.Connected to the municipal supply with no meter etc.
    2)Plugs and lights connected to a 125 amp isolator direct(no switching etc)
    3)DB's and isolators bricked closed.(I am still trying to find all of them)

  2. Thanks given for this post:

    mikilianis (30-Jul-10)

  3. #2
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    For things like that I would shut the place down. You know it. Do it before someone gets hurt. It will bug you the rest of your life(in jail)

  4. Thanks given for this post:

    mikilianis (30-Jul-10)

  5. #3
    Bronze Member mikilianis's Avatar
    Join Date
    Dec 2008
    Location
    Cape Town South Africa
    Posts
    125
    Thanks
    164
    Thanked 8 Times in 7 Posts
    Go for it send some pics and let us unite and anounce the spark that issued the coc as a fraud there is to much of that crap (issuing coc fraudulently ) going around undermines us genuine electricians like if possible use him as an example and prosecute him for fraud.Go for it .
    Mike

  6. Thanks given for this post:

    Sparks (31-Jul-10)

  7. #4
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    We need more of this attitude! We need to stand together about people who are discrediting our occupation.

  8. #5
    Full Member
    Join Date
    Apr 2010
    Location
    Gauteng
    Posts
    59
    Thanks
    6
    Thanked 7 Times in 5 Posts
    These are a few of the problems I have that they dont want repaired.The 16a plug in the hole is unswitched(no e/l or breaker)and the cable sticking out the top is live and cut. Top pic shows close up showing connections.Cable goes to main busbar and supplies store pc/heater/hotplate/kettle etc.Had to cut holes in the walls to find it.Everything is supposedly "mission critical" and cannot be switched off .Thinking or organising a municipal "power failure" and going mad with a sidecutter(probably get fired chop chop but its worth it)There is a lot worse,will take pics and show
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	100_1061 (Small).jpg 
Views:	222 
Size:	34.0 KB 
ID:	1319   Click image for larger version. 

Name:	100_1062 (Small).jpg 
Views:	249 
Size:	44.1 KB 
ID:	1320   Click image for larger version. 

Name:	100_1060 (Small).jpg 
Views:	244 
Size:	29.7 KB 
ID:	1321  

    Click image for larger version. 

Name:	100_1058 (Small).jpg 
Views:	261 
Size:	37.5 KB 
ID:	1322   Click image for larger version. 

Name:	100_1056 (Small).jpg 
Views:	252 
Size:	27.2 KB 
ID:	1323   Click image for larger version. 

Name:	100_1057 (Small).jpg 
Views:	243 
Size:	48.9 KB 
ID:	1324  

    Last edited by Dave A; 02-Aug-10 at 06:52 PM.

  9. #6
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    The first thing I would do is to list the problems and send by recorded mail or email to the general manager as well as the owner along with the info in laymans terms stating why its a hazard. Demand a reply and inform him that now he's aware of the problems he's also personally liable and will also go to jail if he refuses to act and someone gets hurt or killed. Explain that by refusing to act he's putting you in a very difficult position and keep copies of everything.

    Bottom line is if they're prepared to ignore obvious hazards that can result in the death of an employee then they're not the kinda customer you want to work for.

  10. Thanks given for this post:

    greasemonkey (02-Aug-10)

  11. #7
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    Maybe also point out that a DoL inspection is bound to have the operation shut down. Might help shift the line on what really is "mission critical."

    It seems DoL inspectors are increasingly aware of electrical safety issues and I'd guess all it would take is a disgruntled employee (on just about anything ) to encourage a visit.
    Last edited by Dave A; 02-Aug-10 at 07:23 PM.

  12. #8
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Quote Originally Posted by Dave A View Post
    Maybe also point out that a DoL inspection is bound to have the operation shut down. Might help shif the line on what really is "mission critical."

    It seems DoL inspectors are increasingly aware of electrical safety issues and I'd guess all it would take is a disgruntled employee (on just about anything ) to encourage a visit.
    I like that idea. If they're not motivated by someone possibly getting hurt they'll definitely be motivated by the financial implications of getting shut down by the DOL.

  13. #9
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,648
    Thanks
    3,304
    Thanked 2,676 Times in 2,257 Posts
    Blog Entries
    12
    We discovered all the pleasures of scaffolding erection safety requirements when a DoL inspector stopped around a factory trying to bust people operating forklifts without the appropriate certification. My guys just happened to be at the wrong place at the wrong time.

  14. Thanks given for this post:

    greasemonkey (03-Aug-10)

  15. #10
    Gold Member Sparks's Avatar
    Join Date
    Dec 2009
    Location
    Port Elizabeth
    Posts
    890
    Thanks
    20
    Thanked 127 Times in 96 Posts
    I have refused COC's for less. When someone gets hurt and it will happen you will be held responsible. Put it all in writing and send copies to DOL and local supplier. If I am correct this is the tip of the iceberg. The local supplier can shut down the whole supply if an installation is not certified or poses a threat to them

  16. Thanks given for this post:

    greasemonkey (03-Aug-10)

Page 1 of 4 123 ... LastLast

Similar Threads

  1. [Opinion] Debt Advice Agency - How They Work?
    By Debt_Advisor in forum Business Finance Forum
    Replies: 15
    Last Post: 22-Nov-11, 03:16 PM
  2. [Question] CC Advice please
    By pop in forum General Business Forum
    Replies: 8
    Last Post: 09-Jul-10, 08:08 AM
  3. Advice on further action on Golf Course.. (Legal?)
    By emporacci in forum General Business Forum
    Replies: 12
    Last Post: 22-Mar-10, 10:38 PM
  4. Some advice please
    By CharTalbot in forum General Business Forum
    Replies: 2
    Last Post: 12-Sep-08, 05:02 PM
  5. Battery + inverter advice required
    By daveob in forum Electrical Load Shedding Forum
    Replies: 12
    Last Post: 24-May-08, 04:05 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •