Thread: Correct Cable Size

  1. #1
    Bronze Member mikilianis's Avatar
    Join Date
    Dec 2008
    Location
    Cape Town South Africa
    Posts
    125
    Thanks
    164
    Thanked 8 Times in 7 Posts

    Correct Cable Size

    Hi the question I am asking is as follows a sub d.b. is put up + - 20m away from the main d.b. the sole purpose of this s.d.b. is to supply 3 x 11kw motors roughly at 22amps per motor, the motors will be so wired that they start to in sequence so the starting load will be one motor at a time so say the running current of the motors should not exceed + - 66 amps , each motor is individually supplied through a overload relay, would a 16mm 4 core SWA Cable be enough or what do the regs say about this the cable is supported in the air indoors by cable tray, what is the diversity factor for motors sequentially started? Any info thanks.
    Mike

  2. #2
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    you should get the CBI squared program it is a valuable tool for quick calc like this...and it use to be free...and yest according to cbi program it would be fine...beware of the fault level at the panel...if it is close to the sub station.

  3. Thanks given for this post:

    mikilianis (10-Jun-10)

  4. #3
    Bronze Member mikilianis's Avatar
    Join Date
    Dec 2008
    Location
    Cape Town South Africa
    Posts
    125
    Thanks
    164
    Thanked 8 Times in 7 Posts
    Hi Murdock
    I am interested in getting the CBI squared program and also would like more info on fault levels could you provide me with the information to obtaining the program or info relating to cicuit breaker selection Kva ratings and rupturing capacity'
    Thanking You
    Mike

  5. #4
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    you get the program from CBI directly...it is merly a guide line which seems to be the key phrase for the electrical industry...like reasonbly safe

  6. Thanks given for this post:

    mikilianis (17-Jun-15)

Similar Threads

  1. [Opinion] The Undersea Cable, how will it affect all of us?
    By Superscenic in forum Technology Forum
    Replies: 23
    Last Post: 09-Feb-09, 08:09 PM
  2. Lite skin for dial-ups or to reduce page download size.
    By Dave A in forum Administrative issues
    Replies: 9
    Last Post: 08-Jul-08, 10:12 PM
  3. 3rd Undersea cable damaged
    By Chatmaster in forum Technology Forum
    Replies: 2
    Last Post: 07-Feb-08, 09:08 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •