    Supply

    Hi guys I am new to a the forum and would like some help. I have the following scenario.
    On a farm in Cape Town they have a 3 phase supply coming in on to the meters and then to a fuse box and from there to a db in a shed. This db supply’s power to the shed on one phase and two other small houses each on its own phase and each has its own sub db.
    This is not limited to the lights but you see the effect the best, with the light on if you switch anything ells on there's a dip in power and stays like that until you switch it off. This happens in the both houses and in the shed. I have not checked anything yet and would like some fed back what could be the issue. The shed is feed from Eskom

  2. #2
    Suspended
    Join Date
    Oct 2007
    Posts
    2,346
    Thanks
    0
    Thanked 254 Times in 209 Posts
    it could be a neutral problem...loose connection...if it affect all the building i would start at the incomer meter box or main db...check all connections by pulling on the wires or check if the insulation has melted...at the same time check the voltage across all three phases to earth and neutral...then do it at the furtherest point.

    do the lights flicker randomly at any point day or night?

    new or old installation?

  3. Thanks given for this post:

    Dusty (15-Apr-10)

  4. #3
    New Member
    Join Date
    Apr 2010
    Location
    Cape Town
    Posts
    2
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by murdock View Post
    it could be a neutral problem...loose connection...if it affect all the building i would start at the incomer meter box or main db...check all connections by pulling on the wires or check if the insulation has melted...at the same time check the voltage across all three phases to earth and neutral...then do it at the furtherest point.

    do the lights flicker randomly at any point day or night?

    new or old installation?
    Hi Murdock

    No they dont flicker and it is old installation up to the fuse box and from there to the main db and sub db's about 7 years old.

  5. #4
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,923
    Thanks
    576
    Thanked 934 Times in 755 Posts
    Could be undersized cabling somewhere in the system also.

Similar Threads

  1. CISS - Continuous Ink Supply System
    By Loman in forum Technology Forum
    Replies: 42
    Last Post: 23-Apr-18, 09:19 AM
  2. Supply and demand
    By 3x-a-d3-u5 in forum Entrepreneurship and Business Management Forum
    Replies: 5
    Last Post: 29-Jan-09, 08:43 PM
  3. Eco Tubing supply and alarm installation - KZN
    By daveob in forum General Chat Forum
    Replies: 3
    Last Post: 13-Jan-09, 09:10 AM
  4. state of our electricity supply
    By murdock in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 23-Apr-08, 08:20 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •