Hi Murdock,
Have you a particular installation you are enquiring about or are you just asking about the general rules that apply?

Originally Posted by
murdock
12 volt and 230 volt downlighters.
You can't really lump the 12v and 230v lighting systems into one question because they fall under a completely different set of rules.

Originally Posted by
murdock
mounting the transformer?
There's various rules covering the mounting and positioning of transformers.
Code:
7.9.3.1.1 Components shall be mounted in an enclosure, ventilated
where necessary
Code:
7.9.4.4 Transformers, protective devices or similar equipment mounted
above false ceilings that are moveable, or easily accessible, or in a
similar place, shall be mounted on a fixed part of the building such as a
beam, and information shall be given about its presence and location
Code:
7.9.3.3.1.4 The ELV power source shall not be installed above the lamp
or within 200 mm from the lamp to any side unless a heat barrier is
installed between the lamp and the power source.

Originally Posted by
murdock
exposed wiring?
On the primary side (LV) or secondary side (ELV) ??
Code:
7.9.4.1 Primary terminals of the supply source shall be in an enclosure.
Code:
7.9.2.4.1 Bare conductors may only be used in an extra low voltage
lighting installation system if
a) the nominal voltage does not exceed 25 V a.c. or 60 V d.c.,
b) the wiring system is made up of compatible components and complies
as a complete unit with SANS 60598-2-23/IEC 60598-2-23
(SABS IEC 60598-2-23), and
c) the conductors are at least 1 m from the thatch under a thatched roof.
7.9.2.4.2 If both circuit conductors are uninsulated and supplied from a
convertor that complies with SANS 61347-2-2/ IEC 61347-2-2
(SABS IEC 61347-2-2)), the power of the convertor shall not exceed
200 VA. Amdt 1; amdt 3

Originally Posted by
murdock
fuses for the output side?
It depends...
Code:
7.9.3.2.2 Each secondary circuit of a safety extra low voltage (SELV)
supply source (transformer or convertor) shall have overcurrent protection
(see 6.7.1 and 6.7.2). The overcurrent protection may be either by a
common protective device, or a protective device for each SELV circuit.
7.9.3.2.3 A protective device shall be readily accessible unless it is built
into the supply source and is of the automatic resetting type.
7.9.3.2.4 Secondary overcurrent protection is not required where the
maximum output of the SELV transformer is 50 VA, the secondary circuit
conductor is at least 1,5 mm2, not exceeding a length of 2,5 m, and at
least one conductor and its terminals are insulated to prevent a short
circuit. Amdt 1

Originally Posted by
murdock
distance from the transfomer to the lamp?
Can vary but cable must be sized accordingly, see attached table. Also last 200mm must be class H;
Code:
7.9.3.3.1.3 At least 200 mm of the conductors leading from an ELV lamp
holder shall be 180 °C (class H) flexible conductors such as siliconrubber-
insulated conductors. The lamp holder shall also be suitable for an
operating temperature of at least 180 °C. Amdt 3

Originally Posted by
murdock
using a 300 va transformer and sizing the conductors?
Again see attached table, depends on length.