Page 2 of 2 FirstFirst 12
Results 11 to 13 of 13

Thread: DC cabling in metal wireways

  1. #11
    Bronze Member
    Join Date
    Feb 2025
    Location
    SA
    Posts
    112
    Thanks
    4
    Thanked 1 Time in 1 Post
    This is a common question...

    712.542.102 Separate earth electrode
    If a separate earth electrode is provided for the PV array, this electrode shall be connected to
    the main earthing terminal of the electrical installation by main equipotential bonding
    conductors.

  2. #12
    Bronze Member
    Join Date
    Feb 2025
    Location
    SA
    Posts
    112
    Thanks
    4
    Thanked 1 Time in 1 Post
    This clears up the questions about where to install the earth wire.

    PV array bonding conductors shall be run as close to the positive and negative PV array and
    or sub-array conductors as possible to reduce induced voltages due to lightning. See also
    712.521.103.

  3. #13
    Bronze Member
    Join Date
    Feb 2025
    Location
    SA
    Posts
    112
    Thanks
    4
    Thanked 1 Time in 1 Post
    Taking about insulation resistance, take note.

    712.531.3.101.1 Array insulation resistance detection
    The requirements in 712.531.3.101.1 regarding detection and response to abnormal array
    insulation resistance to earth are intended to reduce hazards due to degradation of insulation.
    A means shall be provided to measure the insulation resistance from the PV array to earth
    before starting operation and at least once every 24 h. This can be done by an insulation
    measuring device according to IEC 61557-2, or by an insulation monitoring device (IMD)
    according to Annex C of IEC 61557-8:2014, to prevent a possible high risk of fire.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. [Question] Overhead cabling to outside building question
    By Jimmy657 in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 22-Aug-24, 04:39 PM
  2. Current carrying capacity for DC cabling
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 22-Jun-24, 03:59 AM
  3. Double insulated solar wires in wireways
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 20-Mar-24, 08:37 AM
  4. Fibre and network cables in electrical wireways
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 10-Mar-24, 11:42 AM
  5. Cabtyre cabling not allowed in electrical installation
    By Munnik in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 17-Dec-20, 07:20 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •