    3 Phase PSCC testing.

    Hi All

    Not often I work on 3 phase installations but I'm busy testing a 12 DB, 3 phase installation presently.

    Is this a silly question ?

    I've carried out the PSCC test on the main board from each phase.
    The results are all within spec, however, the results from each phase are not the same. They differ.
    The test report asks for and has place for only one reading.
    Which one is entered on the test report ?

  2. #2
    Diamond Member AndyD's Avatar
    Join Date
    Jan 2010
    Location
    Cape Town
    Posts
    4,945
    Thanks
    582
    Thanked 938 Times in 759 Posts
    Just use the highest reading out of the three.
    _______________________________________________

    _______________________________________________

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,697
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Quote Originally Posted by AndyD View Post
    Just use the highest reading out of the three.
    Thank you, brother. I thought that would be the way to go. Always lekker to get confirmation.

  4. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,697
    Thanks
    127
    Thanked 160 Times in 150 Posts
    Another quick question, brothers.

    There's a 25Kva generator feeding the whole main DB through a change over switch.

    All the sub DB's are fed directly from the main DB.

    My question is ........ Do the sub DB's have an alternate power supply connection or is it only the main DB ?

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,440
    Thanks
    40
    Thanked 337 Times in 283 Posts
    Quote Originally Posted by Derlyn View Post
    Another quick question, brothers.

    There's a 25Kva generator feeding the whole main DB through a change over switch.

    All the sub DB's are fed directly from the main DB.

    My question is ........ Do the sub DB's have an alternate power supply connection or is it only the main DB ?
    Been pondering on the question
    Not sure on the correct answer but was tossing around with the point of control being the decision as to whether it does need or not.

    My tendency is to say the sub DB's do not need a 2nd test report just main DB which goes along with do I need indication at those sub DB's for generator power or utility power and I use point of control/isolation as the measure.

    If I turn the sub DB isolator off and the complete board is off even if gen is running then , No 2nd report .
    I back that decision up with a shopping Centre scenario - There are 100 shops , the complete Centre is run from generator or utility and I am doing the little pie shop of 10sqm - Do I need to request Centre management to do a mains fail so I can take 2 different readings ?
    It would not be practical and at the end of the day I only have one supply cable from the "supplier" ( supplier by definition being Centre Management)

  6. Thanks given for this post:

    Derlyn (28-Feb-25)

Similar Threads

  1. Pscc and earth loop
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 20-Oct-23, 10:04 PM
  2. 3 phase loop impedance testing
    By shaneo in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 01-May-21, 12:55 PM
  3. Single phase generator feeding 1 phase of 3 phase db - discuss.
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 03-Jul-18, 10:06 AM
  4. [Question] PSCC Calculation
    By CeeJay in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 12-Apr-16, 11:30 PM
  5. [Question] Single phase and 3 phase testing course
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 26-Feb-09, 09:14 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •