    Cooker hood connection

    I can remember that sometime in the past, this was discussed, but I cannot find it and cannot remember what the outcome was.

    Today I came across a cookerhood that is connected directly to the load side of the stove isolator.

    The cookerhood has 1,5mm wire and the stove circuit is protected by a 40A circuit breaker. Legal or not ?

    I say no because the conductor between the isolator and cookerhood is part of the installation and it is under rated for the circuit breaker or, is the isolator regarded as the point of consumption in which case it would be acceptable ?

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,372
    Thanks
    38
    Thanked 324 Times in 272 Posts
    I agree - Not allowed due to wire size and also under 6.16.3.2 - cooking appliance circuit over 16amp shall be dedicated
    They talk about a socket outlet in the control unit which was the old type of stove isolator that had a socket and C/Breaker built in to the isolator

    An extraction canopy would also need to comply to the motor section in fixed appliances


    [B]6.16.3.2 Cooking appliance circuits[/B]
    6.16.3.2.1 A dedicated circuit(s) shall be provided for cooking appliance(s)
    that are rated at more than 16 A.
    6.16.3.2.2 One circuit shall not supply more than one permanently connected
    cooking appliance, unless the appliances are in the same room.
    6.16.3.2.3 A cooking appliance circuit may also supply one socket-outlet if
    the rating of the socket-outlet does not exceed 16 A and if the following are all
    contained in one control unit (see also 6.15.4.1):
    a) the socket-outlet;
    b) an earth leakage protection device including overcurrent protection for
    protecting the socket-outlet; and
    c) the switch-disconnector required for the cooking appliance (see 6.16.1).
    NOTE The socket-outlet has to be protected against earth leakage so, unless the
    protection device (see (b)) is in the control unit, the entire cooking appliance circuit has
    to be protected against earth leakage.

Similar Threads

  1. UPS Connection L&E
    By Gene in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 06-Aug-23, 10:14 AM
  2. Connection boxes
    By BEVIN in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 08-Jul-21, 08:00 AM
  3. Stove/cooker connections
    By ians in forum Electrical Contracting Industry Forum
    Replies: 0
    Last Post: 30-Nov-20, 05:33 AM
  4. Can the cooker hood be deemed part of the cooking appliance?
    By Dave A in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 17-Sep-19, 06:18 PM
  5. Cooker connected with a length of 6mm Surfix
    By Darking in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 25-Sep-18, 09:46 AM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •