    Neutral/earth bond Sans 10142

    I have looked and found the reg stating that the neutral shall not be earthed beyond an earth leakage relay.

    Where in Sans does it state that the neutral shall not be earthed on the load side of the point of control ?

    Cannot find it. Help please. I have a dispute.

  2. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,364
    Thanks
    38
    Thanked 323 Times in 271 Posts
    These are the clauses that are relevant to your question



    From SANS 10142-1 ed3.2
    6.1.6 The neutral conductor shall not be connected direct to earth or to the
    earth continuity conductor on the load side of the point of control except as
    allowed in 7.16.4

    7.12.3.1.3 Where alternative supplies are installed remotely from the
    installation, or from one another, and where it is not possible to make use of
    a single neutral bar or neutral conductor which is earthed, the neutral of each
    unit shall be earthed at the unit and these points shall be bonded to the
    consumer's earth terminal (see 6.12.4). The supply from each unit which
    supplies the installation or part of the installation, shall be switched by means
    of a switch that breaks all live conductors operating substantially together
    (see figures P.2 and P.4), to disconnect the earthed neutral point from the
    installation neutral when the alternative supply is not connected
    (see also
    6.1.6).



    Under Distribution systems
    7.16.4 Neutral earthing
    7.16.4.1 Whereas TN-C systems may be implemented along the distribution
    system backbone, the individual service connections at every distribution
    kiosk shall be TN-S.

    7.16.4.6 A TN-S system shall not be converted to a TN-C system.

  3. #3
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,629
    Thanks
    116
    Thanked 153 Times in 145 Posts
    @GCE. Thank you, my brother. Much appreciated.

    That should settle my dispute convincingly. 👍👍👍

  4. #4
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,364
    Thanks
    38
    Thanked 323 Times in 271 Posts
    And then we have NERSA requirements which the naysayers will tell you is not a regulation but it is a requirement for utilities to adhere to as good practice
    Utilities will generally insist on the below

    Extract from NRS 097-2-1:2024

    5.4 Neutral to earth bonding when forming an intentional island
    5.4.1 To prevent a SSEG neutral connection to the the utility neutral through an earth conductor when the SDU opens, the SSEG shall not have a permanent neutral bonding to earth.
    5.4.2 A hybrid system intended to form an intentional island on the load side during utility supply interruption shall open the SDU to prevent unintentional island on the utility side.
    5.4.3 Since the SDU opens the neutral on the utility side, the intentional island neutral shall be bonded to earth within 200 ms after the SDU operation using a neutral to earth bonding unit (NEB).
    5.4.4 The NEB shall open within a time period of 200 ms before the SDU reconnects the inverter to the utility supply.
    5.4.5 The NEB shall consist of an electromechanical switching device rated at the nominal current rating of the inverter.
    5.4.6 The total clearance between the inverter neutral and earth conductors when the NEB is switched off, shall be equal the clearance of the SDU in its open state or more.
    5.4.7 The NEB shall be an internal inverter component or an external device that is activated by a dedicated control port of the inverter.
    5.4.8 The inverter data sheets shall indicate that it contains an internal NEB or a dedicated NEB control port for external devices.
    5.4.9 Installation requirement: Inverters equipped with the NEB control port only, shall have external electromechanical NEBs installed that are SANS/IEC 60947-1 and SANS/IEC 60947-4-1 certified.

  5. Thanks given for this post:

    Dave A (30-Aug-24)

  6. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,364
    Thanks
    38
    Thanked 323 Times in 271 Posts
    Then you often bump heads about point of control and point of supply

    A person you supplies his own electricity is a consumer , not a supplier and therefore the solar system does not have its own point of control as recognized by the regulations


    Definitions from SANS 10142-1
    3.56
    point of control

    point at which a consumer can, on or in any premises, switch off the electrical
    installation from the electricity supplied from the point of supply

    3.58
    point of supply

    point at which a supplier supplies electricity to any premises

    3.77
    supplier

    in relation to a particular installation, any local authority (see 3.47), statutory
    body or person who supplies, contracts or agrees to supply, electricity to that
    electrical installation

    3.16
    consumer

    person who is supplied (or who is to be supplied) with electricity by a supplier
    (see 3.77); or a person who supplies his own electricity
    Last edited by GCE; 27-Aug-24 at 01:36 PM.

  7. #6
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,629
    Thanks
    116
    Thanked 153 Times in 145 Posts
    Wow! Have I got sufficient ammunition now, or what. 🤣👍👍

  8. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,629
    Thanks
    116
    Thanked 153 Times in 145 Posts
    Thank you GCE. Dispute settled thanks to that ammo. At least there are another couple of guys that have been converted to doing it the right way. 👍👍👍

  9. Thanks given for this post:

    GCE (29-Aug-24)

Similar Threads

  1. Earth/neutral bond relay size
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 30-Aug-23, 07:55 PM
  2. Neutral/earth bond for inverters
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 100
    Last Post: 14-Apr-23, 10:52 AM
  3. Where should earth-neutral bond be
    By recre8 in forum Electrical Contracting Industry Forum
    Replies: 5
    Last Post: 06-Jun-22, 03:45 PM
  4. [Question] Poor Neutral/Earth Bond - Stubborn Nuisance Trips
    By Ewaldvdh in forum Electrical Contracting Industry Forum
    Replies: 25
    Last Post: 23-Mar-22, 01:32 PM