    SANS 10142-1 ED3.2

    Hi
    New edition of SANS 10142-1 was published and made available today

    Quite a few grammar errors and technical references to documents updated/corrected with to me a problem area with the deletion of Annex M
    Was not aware that Annex M was being deleted ,but the chatter that has been happening now makes sense - My feeling is the people we ask to represent contractors interests have been sleeping
    A note was added to 7.12.7

    Table of Changes Amdt 2

    Amended to update referenced standards and
    the requirements for voltage drop, busbars
    and earthing, to replace reference to an
    association with a reference standard, to
    delete the clause on external lightning
    protection, and the annex on authority for
    issuing a test report and a Certificate of
    Compliance.


    7.12.7 Additional requirements for photovoltaic (PV) and similar
    installations that provide a supply as an alternative to the main supply

    NOTE For the installation and certification of the dc part of solar or part of an PV for
    single phase installation, refer to the relevant national legislation (see foreword).
    Amdt 2



    Foreword
    Reference is made in the note to 7.12.7 and note 2 to clause 8 to the "relevant
    national regulation". In South Africa this means regulation 5(6) of the Electrical
    Installation Regulations, 2009, of the Occupational Health and Safety Act,
    1993 (Act No. 85 of 1993). Amdt 1; amdt 2
    Last edited by GCE; 12-Aug-24 at 03:50 PM. Reason: extra clauses added

  2. Thank given for this post:

    AndyD (13-Aug-24), Dave A (12-Aug-24)

  3. #2
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,377
    Thanks
    38
    Thanked 325 Times in 273 Posts
    Good to see an improvement with " water heaters " - To me was a problem area where undercounter geysers for basins in small office kitchens where being fed with a socket outlet.
    The red type has been added into the clause

    [I]6.16.2.2 Dedicated circuits shall be provided for water heaters and there may
    be more than one water heater on each circuit. Where a socket-outlet is used,
    it shall be unswitched[
    /I]

  4. #3
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,377
    Thanks
    38
    Thanked 325 Times in 273 Posts
    I do not see the changes in the test report as indicated by the foreword - Maybe someone see's what I am missing

    Foreword
    The test report in edition 3 may be used in parallel with the test report in
    edition 3.2 for a period of 12 months from the date of publication of edition 3.2.

  5. #4
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,645
    Thanks
    122
    Thanked 155 Times in 146 Posts
    Is a kettle a water heater ?

  6. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,377
    Thanks
    38
    Thanked 325 Times in 273 Posts
    Quote Originally Posted by Derlyn View Post
    Is a kettle a water heater ?
    A kettle would be a portable appliance as it is not fixed or plumbed

    instantaneous water heater would be a "hydro boil " type set up or the shower heads you like .


    6.16.2 Water heaters

    NOTE Water heaters include geysers, instantaneous water heaters including units for
    boiling water, heat pumps, solar systems, induction water heaters and the like (see also
    6.16.1). electrode water heaters, steam generators and boilers are not included (refer
    to 6.16.7)

  7. #6
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,377
    Thanks
    38
    Thanked 325 Times in 273 Posts
    The one thing that got me thinking and has not been improved is that the socket outlet for a small under counter geyser would need to be on it's own circuit , which is really bizarre on a element that is less than a KW

    People still conveniently confuse the terminology of dedicated circuit to mean without ELU when it is actually referring to a circuit for water heater only
    ELU will need to be fitted for hot water heater

    6.16.2.2 Dedicated circuits shall be provided for water heaters and there may
    be more than one water heater on each circuit. Where a socket-outlet is used,
    it shall be unswitched


    6.16.2.1 All water heaters shall be bonded in accordance with 6.13 and a.c.
    supply circuits shall be protected by earth leakage protection with IΔn not
    exceeding 30 mA.

  8. #7
    Site Caretaker Dave A's Avatar
    Join Date
    May 2006
    Location
    Durban, South Africa
    Posts
    22,741
    Thanks
    3,322
    Thanked 2,688 Times in 2,265 Posts
    Blog Entries
    12
    So a Speed heat shower head needs to be supplied by a circuit dedicated to water heaters?

  9. #8
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,645
    Thanks
    122
    Thanked 155 Times in 146 Posts
    Thank you, my brother, yes you are correct about me liking the showerheads. Most of my clients who have had them fitted, have thanked me when they see the difference in their electricity bill.
    The difference between a geyser and showerhead is quite noticeable.

    I'm wondering what the thinking was for the socket outlet not to be switchable ? Other than welding type socket outlets, I don't think I've seen "normal" socket outlets that are used in domestic applications, that are unswitched. Maybe the thinking was that one shouldn't use a "standard" socket outlet in a dedicated water heating circuit.

    Your thoughts ?

  10. #9
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,645
    Thanks
    122
    Thanked 155 Times in 146 Posts
    @Dave. That's how I've always installed them, on their own circuit. Most of them, in any case, are rated at more than 16A, but for those that are not will now also have to be on their own circuit.

    A good thing, I'd say.

  11. #10
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,377
    Thanks
    38
    Thanked 325 Times in 273 Posts
    Quote Originally Posted by Dave A View Post
    So a Speed heat shower head needs to be supplied by a circuit dedicated to water heaters?
    That is how I am reading it - Does not seem to be wriggle room - You can have more than 1 on the circuit which helps with heat pumps where you then stick a 1 kw element in the geyser for back up

    6.16.2.2 Dedicated circuits shall be provided for water heaters and there may
    be more than one water heater on each circuit. Where a socket-outlet is used,
    it shall be unswitched

Page 1 of 3 123 LastLast

Similar Threads

  1. SANS 10142-1 (ed3)
    By ians in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-21, 06:29 AM
  2. SANS 10142 Edition 2
    By Karel Kriel in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 02-Jul-17, 08:20 AM
  3. need help cannot find it in sans 10142-1
    By roelie in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-17, 07:46 AM
  4. sans 10142-1:2012
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 8
    Last Post: 23-Apr-13, 05:56 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •