Page 2 of 2 FirstFirst 12
Results 11 to 18 of 18

Thread: Inverter sizing mystery

  1. #11
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,321
    Thanks
    36
    Thanked 315 Times in 264 Posts
    Quote Originally Posted by Dave A View Post
    Your 16 amp reading seems to be a sum of the current on all three phases.
    You multiply by 1.73 when you are using the current for one of the 3 phases ... (and this assumes a balanced load).

    .
    which is what it is 16amp on one phase and it is balanced as it is 4 escalators with 3 phase motors , each escalator drawing 8 amps per phase , confirmed with tong test

  2. #12
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,604
    Thanks
    114
    Thanked 151 Times in 143 Posts
    From the 8A per phase reading that you get for each motor, that calculates to 3.68Kw/ph multiply by 3 = 11Kw.

    Can you confirm if they are 11Kw motors ?

    Ooops !!! a 5.5Kw motor draws approx 7,5A.

    Can you confirm what size the motors are ?
    That will confirm if the AC readings obtained with the tong tester are correct.

  3. #13
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,321
    Thanks
    36
    Thanked 315 Times in 264 Posts
    Quote Originally Posted by Derlyn View Post
    From the 8A per phase reading that you get for each motor, that calculates to 3.68Kw/ph multiply by 3 = 11Kw.

    Can you confirm if they are 11Kw motors ?

    Ooops !!! a 5.5Kw motor draws approx 7,5A.

    Can you confirm what size the motors are ?
    That will confirm if the AC readings obtained with the tong tester are correct.
    Cant get to the motors - Have used 3 different tong testers in different makes as well and the logger - All 4 give the same readings
    Last edited by GCE; 10-Jul-24 at 03:56 PM.

  4. #14
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,321
    Thanks
    36
    Thanked 315 Times in 264 Posts
    These are 2 pics of the inverter screen running on grid in parallel
    On the load side under one with a tong tester I get 25amps and on the other 14 amps

    Attachment 8933
    Attachment 8934

  5. #15
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,604
    Thanks
    114
    Thanked 151 Times in 143 Posts
    There are a million things going through my mind. So many questions.

    Are you any closer to solving the mystery ?

    Sounds as if there's power coming from somewhere else besides the batteries.

    If there were panels involved then one could understand it, but without panels, it is a mystery.

    Is the output of a 3ph inverter in a star or delta configuration?

  6. #16
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,321
    Thanks
    36
    Thanked 315 Times in 264 Posts
    No closer , have spoken to numerous people that are involved with designing including supply and always the same answer - Can't be possible

    Config would be star and there is nowhere else that power can be coming from

  7. #17
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,604
    Thanks
    114
    Thanked 151 Times in 143 Posts
    Still working on this "mystery".

    I dont know 3 phase inverters.
    Dave mentioned that a 12Kw 3phase inverter consists of 3 single phase 4Kw inverters.

    Now the question is, what is the phase voltage of each 4 Kw inverter ? 220v or 380v ?

  8. #18
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,604
    Thanks
    114
    Thanked 151 Times in 143 Posts
    I somehow don't think there's a problem with your physical current readings.

    The "mystery" is somewhere in the power calculation in my opinion. Now to find it.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. [Question] Correct Cable Sizing
    By pmrindel in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 09-Jul-24, 07:00 AM
  2. Sizing a backup system
    By Isetech in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 29-Jan-23, 07:55 AM
  3. Cable sizing for a stove.
    By @SamboLindoh in forum Electrical Contracting Industry Forum
    Replies: 25
    Last Post: 24-Nov-18, 09:37 AM
  4. [Question] Sizing of Electrical components
    By @SamboLindoh in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 16-May-16, 12:08 PM
  5. Sizing Batteries for inverters
    By Tonye in forum Electrical Contracting Industry Forum
    Replies: 1
    Last Post: 24-Feb-16, 11:43 AM