Originally Posted by
Dave A
Office lights are a plug-in system, 5 Amp sockets.
When I got the question, I was absolutely certain on the plug-in part of the replacement - no COC required. Just make sure you comply with the requirements i.r.o. the luminaires -
6.14.1.4 In a lighting circuit, a luminaire that is in a false ceiling or in a roof space 4 m above the floor where there is no ceiling, or in a floor cavity, or in a wall cavity, or in a similar position, may be fed from a socket-outlet which may be unswitched and not protected by earth leakage protection, provided that the socket-outlet
a) complies with SANS 164-3,
b) supplies one luminaire only, not exceeding the rating of the socket-outlet,
c) is accessible for maintenance purposes, and
d) is within 3 m of the luminaire that it supplies.
Or put another way:
You can only supply one luminaire per socket outlet, and the luminaire must be within three metres of the socket outlet.
(Further fine print on the circuit itself applies).
I'm not going to go into the requirements of the circuit itself as that is plainly electrical installation work that must be done under the general control of a "registered person" and requires the issue of a COC.
The replacement of luminaires connected directly into the electrical installation wiring via supply terminals gave me pause for thought though.
The point of consumption will be the supply terminals.
The disconnection and connection of the luminaire at the supply terminal is electrical installation work.
Per regulation 9.4 of the Electrical Installation Regulations, electrical installation work requires the issue of a valid COC.
So it does require the issue of a COC?
Or have I missed some subtlety here?
OK. We know that regulation 9.4 is not being done proactively and consistently by the electrical contracting industry when it comes to small replacement work tasks. But for a while now I've been saying that legitimate electrical contractors are not doing the industry any favours in failing to do so. If the consumer is used to getting a COC whenever a legitimate contractor does any work, they are far more likely to challenge the handyman folk to produce the COC for the electrical installation work they shouldn't be doing...