    Sub db from 3 phase db

    Hi so the original idea was to run a single phase sub db 32 amp for a kitchen from a 3 phase 32 amp db so the guy installed 3 core swa cable but then i told him i dont think 32 amp is going to be enough for the kitchen i would rather go with 3 phase 32 amp. I believe he then added another 2 wires earth and a blue wire in plastic corrugated pipe. I will just flag the other ones the correct collours. Wil i need to have a circuit breaker for 3 phase plus neutral in the main db and wil they need a 3 phase plus neutral earth leakage in the main db becuase of the wires in the corrugated plastic pipe? I will probably put 3 seperate single phasw earth leakages in the sub db.

  2. #2
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    214
    Thanks
    10
    Thanked 21 Times in 19 Posts
    Safest option is the 4-pole breaker, you can then isolate everything in that db with the main breaker. After the main breaker you can put three earth leakages for the three single phase or a main breaker and earth leakage for each phase, these mains can be one pole mains.

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    723
    Thanks
    118
    Thanked 33 Times in 32 Posts
    Also just a flag of something to look into is that the power supply must have the same wireway.

    The exact reg and the terminology I didn't know and can't look up as I am away.

    But my process of thought is you can't have the line in one conduit and the neutral in another, so 3 phase all the phases need to be in the same wireway.



    Sent from my CPH2197 using Tapatalk

  4. #4
    New Member
    Join Date
    Nov 2023
    Location
    South africa
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Ugh that also. Probably has to do with eddy currents wonder if i can just cut a slot between the knock outs for the swa and the two wires

  5. #5
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    214
    Thanks
    10
    Thanked 21 Times in 19 Posts
    6.4.3.5 Each a.c circuit shall be so arranged that
    a) all live cores are in the same wireway, P139
    Not sure if there is any other regs though

  6. #6
    Silver Member
    Join Date
    Jan 2021
    Location
    Orania
    Posts
    214
    Thanks
    10
    Thanked 21 Times in 19 Posts
    Other than the regs I'm sure that if all the wires that belong together exit the wireway together it is easier to know its purpose and safe to assume they have the same source.
    If one wire is here and another there, it makes problem tracing hard. So keep the cables that belong together, together and make it easier and safer for you and the next electrician.

  7. #7
    New Member
    Join Date
    Nov 2023
    Location
    South africa
    Posts
    9
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Sounds like this might be difficult without replacing the entire cable which is now partly under the new building.

Similar Threads

  1. Connecting a 50A Single Phase System to 3 Phase
    By Sean_66 in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 16-Oct-23, 07:43 AM
  2. Changing 3 phase electric DB to single phase. (Switchover etc)
    By Janbez54 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 05-Jul-21, 07:59 AM
  3. Inverter diagram for one phase on 3 phase installation feeding 2 db’s
    By Pieter00 in forum Electrical Contracting Industry Forum
    Replies: 4
    Last Post: 19-Aug-20, 06:44 AM
  4. Single phase generator feeding 1 phase of 3 phase db - discuss.
    By skatingsparks in forum Electrical Contracting Industry Forum
    Replies: 6
    Last Post: 03-Jul-18, 10:06 AM
  5. Three phase to single phase generator advice needed
    By joshthejew in forum Electrical Contracting Industry Forum
    Replies: 3
    Last Post: 08-Apr-15, 10:12 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •