    E Loop and inverters

    Hello

    So I did an E loop of an inverter in island mode, got 2.60 ohms. So that means the current which will flow on an Earth fault is 88 amps.

    The out out breaker of the inverter is a 50amp and wired 10mm.

    But now this 2.60ohms and the current of 88A will not be enough to trip the output CB of the inverter....

    But..... The pass through of the inverter is 50Amps... So if I de rate the output CB to a 40A (so double the rates current trips the main breaker ) we are now loosing 10Amps worth of pass through current...

    So what can be done ? Sure the inverter has its own protection of short circuit and overload but the output CB is not good ?



    Sent from my CPH2197 using Tapatalk

  2. #2
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,400
    Thanks
    98
    Thanked 139 Times in 132 Posts
    Quote Originally Posted by Dylboy View Post
    Hello

    So I did an E loop of an inverter in island mode, got 2.60 ohms. So that means the current which will flow on an Earth fault is 88 amps.

    The out out breaker of the inverter is a 50amp and wired 10mm.

    But now this 2.60ohms and the current of 88A will not be enough to trip the output CB of the inverter....

    But..... The pass through of the inverter is 50Amps... So if I de rate the output CB to a 40A (so double the rates current trips the main breaker ) we are now loosing 10Amps worth of pass through current...

    So what can be done ? Sure the inverter has its own protection of short circuit and overload but the output CB is not good ?



    Sent from my CPH2197 using Tapatalk
    I don't think the problem lies with the breaker, so changing it is not solving the problem.
    The problem is that the earth loop impedance is too high. That's the problem that needs sorting.
    Maybe bigger earth cabling to bring down that reading.

    Have a lekker weekend.

  3. #3
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    724
    Thanks
    118
    Thanked 33 Times in 32 Posts
    Yes ya I thought of that too but it's 6mm earth and the live conductors are 10mm and the neutral earth loop was at 2.30 (somewhere around there )

    So it's the actual electronics of things I think dictating the ohms.

    Often times I have the same earth loop as well as neutral loop and this is what is bringing up this post as I am at a loss and tried contacting others and their thoughts but to no real avail.

    Sent from my CPH2197 using Tapatalk

  4. #4
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    724
    Thanks
    118
    Thanked 33 Times in 32 Posts
    Have a lekker weekend too! Already at the pub to catch up with some mates and then decided to braai some meat later as well. It's Friday nine the less haha.

    Also looks like we doing ok in the cricket so that's great and also the Nedbank golf is on.

    Sent from my CPH2197 using Tapatalk

  5. #5
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,185
    Thanks
    33
    Thanked 293 Times in 248 Posts
    I have had this discussion
    We also get what we deem to be high but when we calculate it is within spec

    Do you have a earth neutral bridge permanent , internal or external relay

    Rmax = V /( 2 x rated circuit current )

    R max = 230/(2 x 50Amp CB ) = 2.3ohm

    This is what you are getting on neutral earth loop

    This is where I have a difference of opinion and never quite got to finish the conversation
    To do a neutral earth loop you place the earth and neutral lead on the neutral , so basically bridging out your earth neutral test leads .

    When testing earth loop on an inverter you are basically at the earth neutral bridge point - Are you not then doing a neutral loop test ?

    In my opinion the earth loop impedance should be zero as I am at the star point and I strongly believe that the results being shown by meters on in actual fact neutral earth loop tests

  6. #6
    New Member
    Join Date
    Oct 2023
    Location
    jhb
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Quote Originally Posted by Dylboy View Post
    Hello

    So I did an E loop of an inverter in island mode, got 2.60 ohms. So that means the current which will flow on an Earth fault is 88 amps.

    The out out breaker of the inverter is a 50amp and wired 10mm.

    But now this 2.60ohms and the current of 88A will not be enough to trip the output CB of the inverter....

    But..... The pass through of the inverter is 50Amps... So if I de rate the output CB to a 40A (so double the rates current trips the main breaker ) we are now loosing 10Amps worth of pass through current...

    So what can be done ? Sure the inverter has its own protection of short circuit and overload but the output CB is not good ?



    Sent from my CPH2197 using Tapatalk
    sorry i am with stupid but how will 88 amps NOT trip a 50 amp breaker, is the breaker faulty?

  7. #7
    Platinum Member Derlyn's Avatar
    Join Date
    Mar 2019
    Location
    East london
    Posts
    1,400
    Thanks
    98
    Thanked 139 Times in 132 Posts
    Good morning brother.
    You are quite correct. 80 amps should trip a 50A breaker, however, when doing a loop test the resistance must be low enough that should an earth fault occur, at least TWICE the current of the protective breaker must flow, therefore ENSURING that the breaker will trip.

    8.6.5.1 At the main switch, the impedance shall be such that an earth fault current double the rated current (or
    higher) of the main protective device automatically disconnects the supply to the installation.

  8. #8
    New Member
    Join Date
    Oct 2023
    Location
    jhb
    Posts
    6
    Thanks
    1
    Thanked 0 Times in 0 Posts
    Thank you brothers, what device are these they are mentioning in the next reg?

    Reg 8.6.5.2 If, for practical reasons, the requirement in 8.6.5.1 cannot be
    complied with
    , as an alternative, an earth fault detection and disconnecting
    device
    may be installed at the supply to the installation. The earth fault
    detection and disconnecting device should be so installed that it operates at
    a current related to the earth fault loop impedance which will limit touch
    voltages to 25 V under short-circuit fault conditions for a period not
    exceeding 5 s

  9. #9
    Platinum Member
    Join Date
    Jun 2017
    Location
    Port Elizabeth
    Posts
    1,185
    Thanks
    33
    Thanked 293 Times in 248 Posts
    It will be an Adit unit - Basically an overgrown earth leakage unit that works from a CT measuring earth current

    Used to be a Bylaw in PE to have fitting on main incomers and then you would set to 10% of current - So a 800Amp supply when you leaked 80Amps to earth it would trip - There are various makes by most CB manufacturers , example link pasted below

    https://strike.co.za/wp-content/uplo...DIT-ECOVER.pdf

  10. Thanks given for this post:

    ACElectric (14-Nov-23)

  11. #10
    Gold Member
    Join Date
    Jun 2020
    Location
    Fourways
    Posts
    724
    Thanks
    118
    Thanked 33 Times in 32 Posts
    I always understood it as an Earth leakage device but say rates at 100mA.

    So a 100mA would be used if the Earth loop is less than 2300ohms. So that if there's is an Earth fault, i.e a kettle had the line or the neutral touch earth then with the Eloop being less than 2300ohm a current of 100mA will flow thus disconnecting the supply. Sure a kettle is on a 30mA but just an example if it was on a dedicated circuit.



    Sent from my CPH2197 using Tapatalk

Page 1 of 4 123 ... LastLast

Similar Threads

  1. Zdb / E loop and Psc on sub DB under ELU
    By Dylboy in forum Electrical Contracting Industry Forum
    Replies: 12
    Last Post: 30-Jan-22, 07:09 AM
  2. Inverters
    By ians in forum Electrical Contracting Industry Forum
    Replies: 2
    Last Post: 27-Jan-21, 05:55 PM
  3. Inverters
    By Sparks in forum Electrical Contracting Industry Forum
    Replies: 16
    Last Post: 15-Jul-15, 06:42 AM
  4. Looking for someone who knows about Inverters
    By HR Solutions in forum Local Ads on TFSA
    Replies: 0
    Last Post: 21-Jan-15, 12:55 PM
  5. Inverters
    By HR Solutions in forum General Chat Forum
    Replies: 33
    Last Post: 11-Dec-14, 01:55 PM

Did you like this article? Share it with your favourite social network.

Did you like this article? Share it with your favourite social network.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •