Hello
So I did an E loop of an inverter in island mode, got 2.60 ohms. So that means the current which will flow on an Earth fault is 88 amps.
The out out breaker of the inverter is a 50amp and wired 10mm.
But now this 2.60ohms and the current of 88A will not be enough to trip the output CB of the inverter....
But..... The pass through of the inverter is 50Amps... So if I de rate the output CB to a 40A (so double the rates current trips the main breaker ) we are now loosing 10Amps worth of pass through current...
So what can be done ? Sure the inverter has its own protection of short circuit and overload but the output CB is not good ?